Corporate Specification
BBS UK
2015.1_version 4
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 2 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
Contents
1.0 GENERAL INFORMATION & PRELIMINARIES ......................................................... 9
1.1 INTRODUCTION......................................................................................................... 9
1.2 GENERAL REQUIREMENTS ........................................................................................ 9
1.2.1 Schedule of Loadings .................................................................................................. 11
1.2.2 Dimensions .................................................................................................................. 11
1.2.3 Room Heights (Clear Finished Heights) ..................................................................... 12
1.2.4 Insurance ..................................................................................................................... 12
1.2.5 Site programme ........................................................................................................... 12
1.2.6 Project meetings .......................................................................................................... 12
1.2.7 Contractors pre-contract planning ............................................................................ 12
1.2.8 Timber Procurement ................................................................................................... 14
1.3 CONSTRUCTION OPERATIONS ON SITE .................................................................... 14
1.3.1 Responsible Sourcing of Materials.............................................................................. 14
1.3.2 Life Cycle Impacts Materials ................................................................................... 14
1.3.3 Execution of Work/Handover ...................................................................................... 15
1.3.4 Site Hoarding .............................................................................................................. 15
1.3.5 Construction Signage .................................................................................................. 15
1.3.6 Health and Safety Board ............................................................................................. 15
1.3.7 Stand for New Opening Banner .................................................................................. 16
1.3.8 Quality control ............................................................................................................ 16
1.3.9 Principal Designer ...................................................................................................... 17
1.4 COST CONTROL ..................................................................................................... 17
1.4.1 Procedures for cost control ......................................................................................... 17
1.4.2 Correspondence, Recording ........................................................................................ 17
1.5 COMPLETION ......................................................................................................... 17
1.5.1 Detailed pre-completion inspection by consultants, contractor and sub-contractors 17
1.5.2 Hand-over to client...................................................................................................... 18
1.5.3 Design and As Built Documentation ........................................................................... 18
1.5.4 Health and safety file/operation and maintenance manual/ tenants handbook ......... 19
1.5.5 Miscellaneous hand-over/ practical completion issues............................................... 19
1.5.5.1 Training of operating and maintenance staff ........................................................ 19
1.5.5.2 Training Schedule ................................................................................................ 19
1.5.5.3 Certificate of practical completion ....................................................................... 20
1.5.5.4 Final accounts/final certificate ............................................................................. 20
2.0 STRUCTURAL FOUNDATION, FLOORS AND WALLS ............................................. 21
2.1 FOUNDATIONS........................................................................................................ 21
2.2 UNFINISHED FLOOR................................................................................................ 21
2.2.1 Reinforced Concrete Floor.......................................................................................... 21
2.2.2 Freezer Compartment Floor ....................................................................................... 22
2.2.2.1 Concrete Slab ....................................................................................................... 22
2.2.2.2 Vapour Barrier...................................................................................................... 23
2.2.2.3 120mm Floor Insulation Lidl to supply and install ........................................... 24
2.2.3 Sales Area Floor.......................................................................................................... 24
2.2.4 Central Floor Drainage .............................................................................................. 24
2.2.5 Stand Alone Trolley Bay Area Surface Finish (External) ........................................ 25
2.2.6 Delivery Area .............................................................................................................. 26
2.2.7 Utility Room Floor ...................................................................................................... 27
2.2.8 Internal Plant Area...................................................................................................... 27
2.3 STRUCTURAL FRAME.............................................................................................. 27
2.4 EXTERNAL WALLS .................................................................................................. 28
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 3 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 4 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 5 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 6 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 7 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
BUILDING SPECIFICATION
Contract dated:
Site:
Between
And
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 8 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
1.1 INTRODUCTION
This specification including attachments is a binding part of a Lease Contract or a
Construction Contract between Lidl and a contracting partner.
In either case, this document details the general performance parameters together with
the detailed finish requirements that the development must conform with.
All requirements described herein must be provided within the scope of the relevant
contract for the contracted sum.
All references to Lidl shall be interpreted as Lidl UK GmbH unless clearly specified as
otherwise, no alternative to Lidl approved suppliers / products / sub-contractors will be
considered or accepted.
Unless otherwise instructed in writing by the Lidl Senior Consultant Construction (SCC),
the development must be designed in full accordance with the Planning Permission,
Building Regulations and Performance Specifications.
All services, which have been described in this specification, must be provided
within the framework of the relevant agreements by the Lessor / Contractor /
Developer at his own expense, with respect to the agreement or by the instructed
specialist company.
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 9 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
The Main Contractor (MC) must obtain Building Regulations approval and pay all fees in
connection therewith. Initial Notice is to be served to:
Email: steve@approveddesign.co.uk
A staged warrant application will be required in Scotland to satisfy the Local Authority
Building Warrant Officer. All submissions will need to be approved by the Warrant Officer
to achieve warrant approval prior to start on site and for all subsequent stages of the
warrant. It is also the Main Contractors responsibility to obtain the completion certificate
for the development to allow the liquor licence application to be finalised. All of this needs
to be achieved in advance of the store opening.
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 10 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
Schedule of Loads
Permanent Actions
Item kN/m2
Roof Sheet (Ondatherm or similar approved) 140mm thick panel 0.16
Hot rolled steel purlins 0.1
Hot rolled rafter beams 0.35
Internal services 0.25
PV panel installation
Variable Actions
Item kN/m2
General access 0.6
Snow 1.0 Min
Wind According to site 1.0 Min
Permanent and Variable actions shall be calculated for the particular roof structure in
accordance with BS EN 1991-1-1.
An additional variable action of 20kg/m2 shall be included in the structural model and
analysis, the purpose of which is to allow for possible future installation of photovoltaic
systems.
The above actions shall be combined with appropriate partial safety factors in accordance
with BS EN 1990:2002 Basis of structural design.
1.2.2 Dimensions
The building dimensions must be strictly in accordance with the relevant layout in the LDGF01
drawings section, only exceptions may be where stipulated by the Planning Permission. LDGF02
The dimensions given here cannot be compromised at any point of the room by conduits LDFF01
/ cable trays, down stands, lintels or wall projections. Dimensions given in the tables LDGF11
below are finished plaster to plaster internal dimensions. LDGF12
Refer to Specification
Warehouse 4.80m
Drawings
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 11 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
1.2.4 Insurance
All certificates to be in accordance with the above mentioned contract documents with a
copy of all valid insurance documents to be issued to the Lidl Senior Consultant
Construction (SCC) prior to start on site.
Two to three weeks before construction work begins on site a pre start meeting is required
between the Lidl Senior Consultant Construction (SCC) and the appointed MC.
The content of the site meetings will be recorded by the Lidl Senior Consultant
Construction (SCC) in a continuous protocol. This is distributed to all participants prior
the following meeting. It is then signed by the MC and the Lidl Senior Consultant
Construction (SCC) to confirm its accuracy. The Lidl Senior Consultant Construction
(SCC) will distribute a set of the meeting minutes to all participants within one week.
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 12 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
The Site Set-Up Plan must be included in the MCs Construction Phase H & S Plan
submitted for approval to the Principal Designer and CDM advisor/Lidl. The Site Set-Up
will change and evolve as the project progresses. This must be discussed at site meetings
and updated as necessary.
All construction sites are required to prepare and implement a Waste Management Plan
as detailed in the Environmental Protection Act.
The Traffic Management Plan must be discussed at the Pre-Start Meeting with the Lidl
Senior Consultant Construction (SCC), Principal Designer and CDM-C and the MCs Site
Agent.
The Principal Contractor is responsible for appointing a Fire Safety Co-ordinator and
Fire Marshalls if necessary.
The MC shall provide a copy of their Site Waste Management Plan detailing:
The target benchmark for resource efficiency e.g. m of waste per 100m or
tonnes of waste per 100m
Procedures and commitments for minimising non-hazardous waste in line with
the benchmark
Procedures for minimising hazardous waste
Procedures for monitoring, measuring and reporting hazardous and non-
hazardous site waste
Procedures for sorting, reusing and recycling construction waste into defined
waste groups either on site or through a licensed external contractor
The name and job title of the individual responsible for implementing the above.
Where applicable a completed copy of the pre-demolition audit of any existing buildings,
structures or hard surfaces must also be provide to the MC.
The MC shall be required, at the initial design stage, to liaise with and seek advice from
the local police Architectural Liaison Officer (ALO) or Crime Prevention Design Advisor
(CPDA) on designing out the opportunity of crime, in accordance with the principles and
guidance of Secured by Design. The MC shall provide feedback and a copy of the scope
of their advice / involvement.
The MC shall confirm the amount of recycled and secondary aggregate, where the
amount specified is over 25% by weight or volume of the total high-grade aggregate uses
for the building.
Such aggregates shall be either:
Obtained on site
Obtained from a waste processing
Secondary aggregates obtained from a non-construction post-consumer or
post-industrial by-product source.
The MC shall allow for applying and complying with and achieving formal certification
under the Considerate Constructors Scheme (CCS).
The contractor shall seek to achieve a CCS Code of Considerate Practice score of
between 32 and 35.5.
The MC will monitor, record and set targets for the following on a monthly basis:
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 13 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
Monitoring shall include checking meters and posting results graphically along with site
energy and water targets, in the site office for the duration of the project. The targets will
be reviewed at each site meeting and will be set using the DTIs Environmental LPI
benchmarks. The MC shall appoint a member of the design team with responsibility for
collection and monitoring this data.
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 14 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
Roof
Upper Floor Slabs (Where applicable)
Floor Finishes/Coverings.
Internal finishes and fittings with low emissions of volatile organic compounds (VOCs) are
to be used.
Height: 2400mm. Main hoarding wall to be RAL 7024. Top and bottom trim (150mm
deep) to be RAL 7038.
A health and safety (H&S) board is required on all Lidl projects, which must be supplied
and erected by the MC in a location adjacent to the site welfare facilities. The sign must
be erected within the first week of the contract, with all required information inserted into
the relevant spaces. It is the responsibility of the MC to maintain and update the H&S
board throughout the duration of the contract.
A canopy trim must be installed over the top of the H&S board to protect from driving rain.
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 15 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
The size of the area to be considered for installing the New Opening banner is L14100mm
x H1300mm. If this size is not possible, an alternative size would be 9600mm x H 900mm.
(To be co-ordinated with Lidl Senior Consultant Construction (SCC)).
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 16 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
1.5 COMPLETION
On specialist systems (non-Lidl Standard), the MC must arrange for the equipment
manufacturer or specialist installer provide a demonstration at the handover of the system
and must include within his Tender costs for all such attendance.
During the course of the construction period, the MC must prepare draft copies of the as
built drawings, operating and maintenance manuals for submission to Santia for
comments prior to the final document being issued to Lidl.
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 17 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
All O&M manuals must be completed and issued to Lidl at practical completion.
All electrical tests (carried out by an NICEIC approved electrical contractor) must be
carried out in accordance with BS 7671 and fully recorded; all test results must be issued
as part of the operating and maintenance manuals.
The Contractor must prepare full maintenance and spares schedule for all installed
systems and include this in the O&M manuals.
The Contractor must arrange for a services engineer to be available on site on day of
store opening 1 No. Service Engineer with working knowledge of the project, with tools
for emergency repair or maintenance on any mechanical or electrical item of equipment
installed as part of the contract works.
The Mechanical Electrical Contractor must provide 2 No. hard copy sets and 2 No.
electronic of Operating and Maintenance Manuals incorporating as-built drawings, all to
be completed at least 1 week prior to handover.
An electrician and auto door engineer must be on site on the store opening day.
Access to the goods delivery area must be guaranteed on PC. External facilities, external
rendering and/or cladding have to be completed, as well as the entrances and exits for
customers, including pavements and parking spaces. Scaffolding, all plant, machinery
and building material have to be completely removed prior to PC1.
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 18 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
Electrical Installation certificate: proof that installation complies with IEE Regs
and was carried out by an NICEIC installer.
Emergency lighting certificate
Mechanical installation certificate in accordance with CIBSE Regs.
Gas installation certificate (carried out by a Gas Safe Register installer)
Utility services, heating, ventilation, sanitary, electrical
Area list
List of expenses/ Data list
Acceptance certificate for BMS technology
Handover protocol (PC checklist), list of defects
Other technical inspection documents
List of all participating sub-contractors and craftsmen including company name,
address, phone, fax and a contact name.
On acceptance and handover of the ready for occupancy property these documents have
to be handed over to Lidl complete as two sets of hardcopies and two sets of electronic
devices (CDs) containing all documents scanned or saved in PDF format, as well as all
drawing information saved in DWG format.
1.5.4 Health and safety file/operation and maintenance manual/ tenants handbook
It is essential that the O&M Manual is handed over promptly on completion of the works
and includes all information set out in Lidls Corporate Specification. The O&M Manual
must incorporate the information required for the Health & Safety File and compliance
with the Construction Design and Management (CDM) Regulations.
The MC shall be responsible for developing a Building User Guide. The guide shall be
developed in compliance with the Breeam criteria.
The Building User Guide should be specific to the building and should include as a
minimum the following:
Overview of the building and its environmental strategy
Building services overview and access to controls
Pre-arrival information for visitors. E.g. access and security provisions
Safety and Emergency provisions/instructions
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 19 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 20 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
Air tightness testing is to be carried out by the Main Contractor. The Contractor will
appoint the air tightness specialist and arrange for the test to be carried out at a time
which does not impact on the program of works in the run up to completion of the store.
The Air tightness result is to be less than 4.0m3/hr/m2 of measured envelope area at a
test pressure of 50Pa.
2.1 FOUNDATIONS
The foundations shall be designed to support all of the superstructure loadings, including LDGF01
service loading, with due regard to the ground conditions, and in accordance with the LDID01
relevant Codes of Practice and Building Regulations.
The gable containing the shop front glazing must be constructed without steel beams or
columns visible behind the windows.
The design loadings for the floor slab and sub-base shall be 10kn/m2 and shall be capable LDGF01
of withstanding a moving load of 5,000kg (as represented by fully loaded battery operated
pallet trucks). The load bearing capacity of the cash room slab must be sufficient for the
installation of a safe (approx. 1,100kg over 850mm x 850mm Base x 1350mm Height).
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 21 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
The floor slab shall be constructed of reinforced concrete C28/35 (as per structural LDID01
calculations) with a smooth finish, laid to a tolerance of 5mm within overall datum level.
The slab shall be laid in a single pour with expansion joints to the perimeter only and laser
levelled ready to receive an un-bonded sand / cement screed and ceramic floor tile finish.
The floor slab is to be poured to a depth of -75mm below FFL to provide for the tiling
finishes.
Underneath the floor slab, a thermal insulation layer of 60mm thickness using high- LDID01
performance rigid urethane board (BASF Styrodur or similar, minimum 0.5 N/mm load LDGF01
bearing) shall be installed in a strip of 4m width around the external walls of the building, LDGF02
and 8m wide across the entire till area (see standard detail drawings). Additional
gas/hydrocarbon protection may be required, depending on the findings of the SI report.
However, a DPM of minimum 2000 gauge polythene lapped and taped is a necessity.
A 1400mm wide x 2000mm long x 120mm deep recess shall be formed in the slabs to LDID02
allow for the installation of the sluice. There shall be a 100mm gradient from each of the
4 sides to the centre of sluice, formed with screed and tiles.
Internal drainage pop-ups shall be provided to the Sales Area Floor, BUF, Bakery LDGF01
preparation room, canteen, toilets, sluice, refrigeration plant area and utility room. The LDFF01
falls of all connections should be in accordance with relevant British Standards. The
setting-out of contraction joints in the floor slab of the Sales area, if required, should only
be undertaken in agreement with Lidl and the tiling company. 2no. foul drainage pop up
100mm diameter shall be provided to the rear of warehouse for possible future
construction of additional customer WCs.
Samples must be taken during all structural concrete works, and the compressive
strength tested in an approved laboratory (numbers of test samples to be agreed with Lidl
regional construction office at the construction pre-start meeting). Results are to be
forwarded upon receipt, with copies contained in the handover folder.
A 25cm high concrete upstand at the base of the walls shall be constructed to all LDID01
Warehouse and delivery area walls.
The floor structure is to be designed so that the finished floor level of the Freezer
Compartment is the same as that of the remainder of the building.
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 22 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
The Freezer Compartment floor build up consists of the following layers, from bottom to
top:
1. Concrete Slab
2. Vapour Barrier with tape seal
3. 120mm Floor Insulation panel with V2A edition stainless steel plate to R11 Slip
resistance.
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 23 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
The floor channel will be constructed under the tills at a distance of 2.950m from the front
windows. Two 150mm diameter ducts for data cables must be formed in a closed floor
channel. The channel will link the tills area to the IT Room on the first floor.
One 150mm diameter power duct will be required from the Cash Room to the tills area.
This can be formed with a deepening in the concrete floor. Three 70mm diameter ducts
are required at various locations in the Sales Area floor. These ducts can be formed with
a deepening in the concrete floor.
500 x 500mm duct chambers with 600 x 600mm floor plates will be constructed in
accordance with LD-GF-05
All waste water drainage pipework taking discharge from the preparation area and freezer
room, inclusive of the floor gulley are to be combined in a 100mm diameter pipe.
All floor drains in the Sales Area, Bakery Preparation, Freezer and Warehouse are to be
equipped with an odour trap and silt trap to aid cleaning. The cover needs to be
removable at all times without any tools (no screwed in or similar) for maintenance /
cleaning purposes.
All drains are to be fully sealed and designed to be fully air tight and waterproof.
All pipework is to be suitable dimensioned in order to adequately deal with the volume of
water discharged from each area and in accordance with specification or details provided
by the supplier of the equipment and bakery preparation sink unit.
All waste water pipes supplied and installed from the bakery ovens are to be
manufactured in steam resistant, temperature sensitive, acid- and alkali-resistant
materials again in accordance with the oven manufacturers literature.
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 24 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 25 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
asphalt areas. Bull nosed or rounded kerbs are not to be used. Refer to Specification
Drawings.
The floor slab detail to the front edge of the loading platform must accommodate a full LDRL01
width galvanised steel c-profile. The steel c-profile shall be cast into the concrete floor
slab with relevant fish-tails or other means of securing the profile into the slab (in
accordance with structural design).
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 26 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 27 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
Single Skin Construction with 365mm Fire Clay Insulated Building Blocks (Poroton LDID01
cellular block T-9 interleaved) is the only approved construction method. Any alternative
to this must be authorised in writing by the Lidl Senior Consultant Construction (SCC). All
external walls are to be constructed as load bearing and shall be designed and
constructed to achieve minimum U-values less than 0.25 W/m2K.
In accordance with the heat calculations and to prevent cold bridging, the concrete LDID01
columns on perimeter walls shall be finished with a hard insulation board on the external
face. The insulation board must finish flush with the external face of the block. This
allows for the columns to be hidden behind a monolithic render finish. The walls must be
rendered with Bauprotec RHS render system or similar approved. Breathable paint is to
be used for all walls.
The walls shall be finished with exterior render 20mm thick. The interior walls are to be
plastered with a 15mm flush finished lime/cement plaster. The walls must be rendered
with Bauprotec 850M render system or similar approved.
The head and posts at the delivery door (housing the sectional door) must be constructed
using reinforced concrete, irrespective of the construction method of the remainder of the
building. The head and posts must be insulated to achieve the minimum required U-value
of the external walls of 0.25W/m2K.
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 28 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
The head and posts for the following doors (housing for the door frame) must be
constructed using reinforced concrete, irrespective of the construction method of the
remainder of the building. The head and posts must be insulated to achieve the minimum
required U-value of the external walls (0.25W/m2K):
External Walls Door Reference Nos D-05, D-06, D-07, D-10, D-11, D-12, D-17
Internal Walls Door Reference Nos D-09, D-18, D-35
A waterproof / splash-proof plinth base must be formed up to 450mm high (measured LDID01
from FFL external ground) around the building perimeter with a final coat of diffusion open
light weight, water-resistant float finish render in 1mm graining finish applied to polymer
scratch undercoat (RIW or liquid bituthene) watertight/ resistance for ground water
pressure up to 7BAR (70m water column).
If required, expansion joints, day joints, edges and corner beads are to be either heavy/
hot-dip galvanised or stainless steel profiles used for plaster thickness of 10-15mm.
Note: surface preparation of Fire Clay Insulated Building Blocks block work and concrete
block work: surface must be solid, able to carry load, clean, frost-free and dry, free of less
solid surface layers, dust, loose parts, and paint remainders.
The surface of Poroton and concrete blockwork must be prepared for plastering as
follows: surface must be solid, clean, frost-free and dry, free of dust, loose parts, and
paint remainders.
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 29 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
Correct finish: clear delineation between white and grey elements using appropriate
beading.
2.4.2 Painting
The walls shall receive exterior masonry paint, colour white RAL 9010 and grey RAL 7038
(plinth). The facade plaster is to form a waterproofed band circulating around the entire
base of the building, height 450mm above finished footpath level running parallel to the
eaves, colour grey, RAL 7038. In the case of the delivery ramp, the top of the banding
shall remain level across the entire loading bay, with the bottom tapering down to follow
the ground level. The banding must be formed with a final coat of diffusion open
lightweight, water resistant float finish render in 1mm graining finish applied to polymer
scratch undercoat (RIW or liquid bituthene) watertight resistance for ground water
pressure up to 7BAR.
LDID01
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 30 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
A 100mm cavity shall be formed, incorporating EPS insulating boards secured to the
inner leaf with proprietary plastic retaining clips.
The inner leaf shall be formed from concrete blocks having a minimum crushing strength
of 7.0N/mm or a 240mm fireclay insulated building block (Poroton cellular block). The
blockwork must be of sufficient thickness to accommodate chasing of all electrical cables,
plumbing, waste pipes and any other required services.
The cavity wall ties shall be of stainless steel vertical twist type, set at 900mm centres
horizontally and 450mm centres vertically increased around openings, and in accordance
with the manufacturers instructions and Building Regulations. The cavities to all reveals
shall be closed.
If the structural calculation allows, the prefabricated wall may be constructed without load-
bearing supports.
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 31 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
The dividing spine wall between the Sales Area and the Warehouse / Welfare Area is to
be constructed with one leaf of 365mm Poroton blocks and the concrete columns shall
be load bearing. Where columns are required, they must be finished flush to the wall.
Under no circumstances will a visible steel joint (bolted or plated) be accepted on the
Sales floor or the Warehouse floor.
The dividing wall between the male and female staff toilets may be drywall construction;
however they must be double boarded on both sides using 12.5mm waterproof
plasterboard. This also applies to the false wall that covers the toilet frames.
The wall between the disabled/customer toilet and the Warehouse must be constructed LDWA03
using minimum 175mm thick blockwork. No dry-wall construction is permitted other than
indicated above.
Around the full perimeter of the Warehouse delivery area, a 250mm height x 225mm wide LDID01
up-stand shall be formed to provide improved crash impact protection properties. This
up-stand must be formed in reinforced cast in-situ concrete, with an adequate layer of
insulation, not to the inner leaf, to meet an overall wall U-value of 0.25 W/mK
Internal blockwork wall finish to be lime cement plaster in 1 layer to min 15mm thickness
with 0/1.25mm graining finish to BS 1191: Part 2.
In order to install the steel cabinet for the intruder alarm system (IAS) a concrete pad,
measuring W 1,000 x full height, positioned in the IT Room wall, must be constructed.
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 32 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
All interior walls have to be painted with water-resistant emulsion paint. Colour: white,
RAL 9010 to comply with BS 6150. (Exception: tiled areas).
If using a prefabricated construction method and no interior render is applied, the walls
have to be sealed and smoothed over to cover unevenness and connection points before
painting.
The internal Sales Area walls shall be painted grey from 2.4m to roof. Paint colour shall
be RAL 7024.
Lidls Direct Trade Contractor will install the surround between PC1 and PC2. The Main
Contractor must provide all appropriate lifting equipment to the Direct Trade Contractor.
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 33 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
A flat 2.0m overhang with an overhead clearance of at least 4.5m (measured from FFL
delivery lane/ramp) must be constructed over the delivery door.
The Main Contractor must allow for an additional 0.2kN/m2 permanent load to cater for
the possible future installation of a photovoltaic system.
The main roof must be designed as a Mono Pitched Warm Roof. The roof load-bearing LDEL01
structure must be built in steel beam construction in accordance with the structural LDEL02
requirements and calculations. The support is on the exterior walls and the Sales / LDEL03
Warehouse spine wall. The pitch shall be a maximum of 5. Maximum height on the front LDEL04
elevation shall be 7.57m and 5.28m on the rear elevation. The lower side of the roof and LDEL05
the rainwater downpipes are located to the rear side of the store. Refer to Section 1.2.1 LDEL06
for details of the roof loadings to apply. LDEL07
LDEL08
The complete roof structure is to be formed using a 762mm rafter beam (LOF 14) and LDRP01
intermediate 152mm steel purlins (I-Beams). The analysis and design of this roof LDRP02
LDAD01
structure is to be carried out by a specialist supplier and in accordance with EN 1995-
LDAD02
1:2004 and relevant sub clauses of the National annex. Each individual steel section shall
LDAD03
be designed with a strength class in accordance with current Eurocodes.
LDAD04
LDAD05
The use of cold-formed purlin sections is not permitted. The structural roofing envelope LDAD06
must be fixed directly to the steel beam roof structure. All roofing elements (structure and LDAD07
envelope) must be painted white (RAL 9010). LDCS01
LDCS02
All steel to steel bolted and welded connections to the main rafter beams must be hidden. LDCS03
The rafter beam in the Sales area must be formed of one continuous length. Bolted
plates, welded face plate and/or back-to-back end plate connections will not be permitted.
Beam to column connections must not be constructed with a visible haunch bolted
connection to be provided with all bolts concealed behind cladding so they are not visible
in the Sales Area.
152x152x37UC purlin beams are required between the main rafter beams to carry the
roof panels. The purlin beams must be located centrally over the aisles in the Sales Area.
The steel layout must be designed in accordance with the Lidl sales vision.
Heating and ventilation units shall be installed in the internal Plant Area at first floor.
Access to the first floor shall be via a concrete stairs located in the lobby between the
Warehouse and the Welfare Area. An alternative escape ladder is located at the opposite
end of the internal Plant Area. All doors in the first floor must be self-closing and in
accordance with the Fire Engineering requirements.
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 34 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
The characteristic imposed load on the delivery bay roof must be greater than or equal to
10kN/m2.
Rain Water Down Pipes fitted with emergency overflows are to be installed as per the
standard detail drawings.
The delivery area roof must be of flat roof construction. Roof covering shall consist of
Sika Trocal Membrane Roof over concrete screed over insulation over concrete roof. Big
feet spreader plates must be installed to suit plant installation.
LDEL01
LDEL02
LDEL03
LDEL04
LDEL05
LDEL06
LDEL07
LDEL08
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 35 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
The gables, high sections of the wall elevations and the soffits are clad using a rainscreen
system finished with Alucobond metal cladding.
The overall wall cladding construction is to be designed and constructed to achieve the LDAD02
LDAD01
required U-value as a minimum and be fully compliant with the requirements of building LDAD03
LDAD02
regulations and in accordance with BRE recommendations. Front and rear elevations do LDAD04
LDAD03
not require the full build up. The ramp side gable elevation requires the full build up. LDAD05
LDAD04
(BRE report 1989: Thermal Insulation: Avoiding Risks). The rainscreen is to use a LDAD06
LDAD05
concealed SZ20 fixing system with stainless steel fixings and is to incorporate a fully LDAD07
LDAD06
adjustable support system mounted onto a vertically laid structural tactray 90 x 500mm.
Joints and penetrations to provide an effective vapour control layer and weather line.
Insulation to comprise 120mm of mineral wool with a Lambda value of 0.035 W/m2K
compressed to 90mm within tactray. Additionally, a 60mm thick layer of mineral wool
insulation with a Lambda value of 0.035 W/m2K is to be used in front of tactray to
minimise cold bridging. A breather membrane must be installed (rampside gable
elevation only). Joints to be fully taped around penetrations to provide effective vapour
control layer and weather line. The cladding shall be finished in 4.0mm thick Alucobond
in silver metallic 500 (RAL 9006). The cladding is to be installed in accordance with the
manufacturers recommendations. The standard panel size is to be 4180mm x 708mm,
colour White Aluminium RAL 9006. Vertical joints shall have hidden fixings. The
Alucobond panels are fixed to the structure in accordance with the standard detail
drawings.
Note: Where the Alucobond cladding is fixed directly to the Poroton block no insulation
or vapour barrier is required, providing the Poroton block is rendered with a waterproof
render as normal. If the rear gable is not fully sealed with a Poroton wall and waterproof
render, the full Alucobond build-up is required (i.e. vapour barrier, insulation and liner
sheet).
Stainless Steel Fixings only are to be used for the fixing of Alucobond panels. The visible
part of the fixing is to be powder coated to match the Alucobond. The aluminium support
brackets must be fixed to the concrete band beams using M10/M12 Rawl bolt fixings or
similar approved
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 36 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
The cladding joints in the main elevation should continue into the soffit and fascia panel
at high-level. On the gable elevations, the joints in the high-level soffit / facia panel should
be positioned in line with the middle of the main panels.
An F shaped bracket should be used to detail any points where Alucobond is fitted to a
store wall / column. These brackets must be of the same coloured finish as the
Alucobond. See detail below.
Sun blinds are required to the front window elevation at eaves and at 3.3m level in
accordance with the drawings. Louvres are required to the high level slot windows if the
side elevation is southeast, south or southwest facing.
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 37 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
4.1 FLOORS
All rooms (except Utility Room and I.T. Room) including the entrance lobby must be fitted
with ceramic stoneware floor tiles in accordance with DIN EN 176.
Quality Plan level: Top Quality
Slip Resistance: minimum R 9 (R10 in Bakery Prep. Area)
Warehouse
Colour: Flakes
Size: 300mm x 300mm, 15mm thick
Welfare Areas
Colour: Anthracite Grey
Size: 300mm x 600mm, 15mm thick
Stairs
Colour: Anthracite Grey
Size: 300mm x 300mm, 15mm thick
Tiling must be carried out in accordance with the manufacturers tiling guidelines
regarding the vibrating method and offset laying method. No threshold bars to be used at
internal door thresholds. All tiling must be continuous from room to room. All exterior door
threshold bars to be in place prior to tiling works commencing. All doorframes complete
with threshold bars where required have to be installed prior to tiling works
commencing. Changes in tile sizes to be delineated with a stainless steel angle fixing.
The Main Contractor will be responsible for procuring a specialist subcontractor to lay the
floor tiles. All areas with the exception of the I.T. Room, Internal Utility Room and Freezer
Room are tiled. The corridor between freezers is also not tiled.
Note: R9 Slip Resistance for general areas and R10 Slip Resistance for the Bakery
Preparation Area.
The tiling subcontractor must adhere to the full specification for the floor tile laying
requirements.
Tiles may only be laid once the shop front, roof and building are completely sealed.
Temporary weather-proofing such as plastic sheeting is not permitted. All doorframes
(complete with threshold bars where required) have to be installed prior to tiling works
commencing.
The tiled area must under no circumstances be loaded within the first 7 days after
installation. After 7 days, the tiled area can then be accessed by foot, light ladders or light
scaffold standing on sturdy plywood boards. Full load bearing capacity can only be
assumed 14 days after installation. The Main Contractor must ensure that these
restrictions are fully complied with, and the Construction Programme designed to
incorporate same.
Tiles are to be laid in a standard bond pattern with grout lines running perfectly straight
across the width and length of the store. A dark grey grout must be used with the
anthracite grey tiles.
The compressive strength of the screed must conform to DIN EN 13318: 2000 with a LDGF01
strength grade of minimum CT-C25-F4 according to DIN EN 13813: 2002 and LDGF02
respectively DIN 18560-4: 2004. A plastic membrane is to be laid on the top of the LDGF04
concrete subfloor prior to tiling. LDFF01
LDFF03
The requirements on the evenness of the ceramic floor tiling noted within DIN
18202:1997-04 (Table 3, Column 3) must be complied with. Over a distance of 4 metres,
the difference in levels must be less than 10mm, and less than 4mm over a distance of
1metre. A tolerance of 0.5mm difference in height between neighbouring tiles is to be
achieved. At the entrance pod and at the external doors (drivers door, sectional door at
delivery ramp), tiles must not project further than the external doors outer limits. Full floor
tiles should be installed along the outside walls and sluice. A 300x600mm cut tile must
be installed between the door and entrance mat.
The concrete stairs must be tiled in accordance with the drawings and details. LDCD03
Appropriate tactile and vision impairment augmentation techniques in accordance with
the Building Regulations must be adopted.
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 39 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
The tiled floor must be protected with Visqueen and hardboard or Correx with taped joints.
All floor protection must be maintained during the course of the works to safeguard the
finished surface. Protection should only be lifted one week prior to Practical Completion.
Floor tiles must be cleaned to a high standard once complete (agreed on inspection by
the Lidl Senior Consultant Construction (SCC)). Cement remover must be used. The floor
must be cleaned and any stained tiles are to be cleaned or removed. The Main Contractor
must ensure that the floor is thoroughly cleaned again prior to handover.
A neat white silicone bead must be used to seal between the top of the skirting tile and
the plastered wall.
The trolley bay steelwork must be fitted directly onto the concrete sub base and the
paving bricks fitted neatly around same. Any voids shall be neatly filled with coloured
grout.
4.1.4 Matwell
An enlarged, heavy duty matwell, 3000mm wide x 3000mm long is to be built into the new LDEP01
Entrance Pod by the Tiling Contractor. The position of the matwell must be co-ordinated LDEP02
with the tiler and agreed with the Lidl Senior Consultant Construction (SCC). A 600 x LDEP03
300mm tile must be laid between the matwell and the door. The tile must finish under
the sliding door (i.e. no tile must be visible outside the closed door) with stainless steel
angle / edge trim installed between the junction of tiling and external block paving.
The location and extent of the joints must be approved in writing by the Lidl Senior
Consultant Construction (SCC). The maximum permissible tiling field size is 200 sq. m.
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 40 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
the Dock Leveller Platform, finishing flush with the outside edge of the sectional door.
The concrete subfloor in the area where the plates are to be installed must be at least
80mm under FFL.
Where applicable, one row of 300mm x 300mm Stelcon anchor plates are to be installed
at the entrance and exit to all delivery and back of house goods lifts.
No steel anchor plates must be visible from outside when the door is closed.
The MC must design the floor slab detail to the front edge of the loading platform to
accommodate a full width galvanised steel c-profile. The steel c-profile shall be cast into
the concrete floor slab (in accordance with structural design) and painted yellow with
black diagonal stripes (45).
At the threshold between the floor tiles and the exterior block paving, an L-angle steel
profile must be fitted in line with the sliding doors.
Prior to any work commencing the MC must co-ordinate the tiling contractor and the lobby
installer in order to achieve the correct position of the threshold.
Along the entire width of the sectional door, one row of Stelcon Anchor Plates, stainless
steel (3mm thickness) must be installed flush with the adjacent surfaces. Plates should
be located in line with the outer edge of the sectional gate.
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 41 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
Staff Room
A splash back must be installed behind the work surface in the kitchen of the staff room. LDWA02
- Same material as cabinet front
- Height +600mm above kitchen units
- Optional coloured wall (to be agreed with Lidl UK)
WCs
Full height tiles in WCs.
Wall tiles: Grey beige
300 x 600mm, horizontally installed with linear pattern (grout colour: light LDWA03
grey)
Lowest row of wall tiles in colour of floor tiles
Tiles first class quality
Abrasive category 2
Junction between wall tiles and ceilings to be sealed with mastic joint.
Sluice
A splash back must be installed at the wall above the area of the sink/hand wash basin, LDID02
dimension W ca. 9000mm x H 1800mm, tiles 600mm x 1200mm.
The area of the floor drain beneath the grating must be tiled (with floor tiles) to form a fall
leading to the gully.
Around the sluice a border of 300 x 300mm floor tiles are to be laid.
All junctions around the sluice wall and floor tiles are to be suitably sealed with grey
mastic.
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 42 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
The inside of the sluice must be tiled with the approved R9 floor tile. The walls around
the sluice area are to be tiled with the same tile as per the Bakery according to the
dimensions (600mm x 1200mm) shown on the detail drawings. The joints shall be filled
with light grey grout. All junctions around the sluice wall and floor tiles are to be suitably
sealed with grey mastic.
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 43 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
Transitions between tiles, walls, and PVC have to be sealed in a permanently elastic
manner. An additional silicon bead should be installed between all walls and the ceiling
grid.
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 44 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
The Freezer Compartment Walls shall consist of insulated sandwich elements; these
elements are to be:
- 170mm in thickness
- Manufactured from Polyurethane rigid foam with a U-value = 0.138 W/(mK)
- With an outer skin of zinc-plated steel sheet
- Colour RAL 9002
- Certified Food Safe
- All rivets to be finished with white Food Safe Caps.
- All joints to be sealed with white silicon sealant
Coving is to be installed where the wall meets the ceiling and where the walls meet each
other.
Penetrations into the Freezer Room for the pipes of the evaporator are to be determined
in consultation with the Lidl refrigeration system supplier / installer and their
specifications.
All penetrations of the freezer room envelope for cabling or pressure release valves must
be appropriately sealed to prevent the ingress of moisture and air.
The wall between the bakery and the freezer is a F60 minute fire wall between two
compartments, the Sales Area and the Warehouse Area. The freezer door located in this
compartment wall must be an F60 door. The door must be a self-closing F60 fire door
with proprietary fire strips located in the door frame.
4.3.2 Ceiling
The ceiling of the freezer shall be at a height of 2.6m above the Finished Floor level. The LDBD02
ceiling panels will be the same insulated as those used for the walls. LDBD03
LDBD04
4.3.3 Door
Four (4) Freezer Compartment doors must be installed in the dividing walls of the LDGF01
freezer/chiller area. The doors must be a mechanical sliding door with integrated frame LDGF02
LDBD02
heating. The door is to be fitted with square profile bump protection.
LDBD03
The doors must have clear measurements of 1350mm (W) x 2250mm (H) and fully
wrapped in 0.8mm brushed stainless steel. They must have a bow type handle of chrome
nickel steel.
Strip curtains of transparent plastic material are to be fitted between the Freezer
Compartment Door and the Freezer Compartment. Each curtain strip must overlap the
neighbouring strip, i.e. there should be no gaps between any of the curtain strips.
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 45 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
to be located directly over the door or the Freezer access aisle. Two Equalising Valves
must be fitted with a fault indication system with an indicator on the Sub Distribution Board
All safety installations must be checked with Lidl Procurement and the refrigeration sub-
contractor.
The ceiling grid structure main runners shall be spaced at 600mm centres and be
suspended from the structure or soffit using pre-straightened 2mm diameter HDG steel
wire hangers at 600mm centres. The first hanger shall be no more than 450mm from the
perimeter. The main runners shall run down the length of the room and be joined end on
by means of an integral splice. Splice connections shall be supported within 150mm with
a hanger and shall be staggered across the store ceiling area. Hangers shall be fixed to
the structure or soffit using fixings appropriate to the structure or soffit. All suspending
wires should be subject to tension and should not be suspended at a slant.
The suspended ceiling shall form a full fire barrier to a resistance level of F30. The
instructions of the manufacturers must be complied with in this regard, and the Main
Contractor is fully responsible for achievement of this property.
The Main Contractor shall take all responsibility for replacing any ceiling tiles damaged
by Lidl direct contractors. The Main Contractor must manage the Lidl direct contractors
appropriately to ensure same is minimised together with the support of the Lidl Senior
Consultant Construction (SCC). The Main Contractor may pursue the Lidl direct
contractor directly for losses as a result of this.
If the standard of concrete ceiling finish is not acceptable, a suspended ceiling must be
installed at the request of the Lidl Senior Consultant Construction (SCC).
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 46 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
must not be used under any circumstances as the air chambers within the blocks will be
damaged.
4.6.1 General
Connection joints between pod / door / window sections and the structure are to be sealed
as thermally insulating and permanently elastic. Further jointing by request of the Lidl
Senior Consultant Construction (SCC). Mastic finish is to be anthracite or RAL 7024.
All glazing panels must be double-glazed, with laminated safety glass. The glazing units
shall be manufactured from 2 x 8.8mm panes with a 16mm Argon-filled cavity, etched
with approved BS Kite safety markings. Internal pane to have a low-E soft coating to the
internal face so that the overall glazing unit can achieve a minimum 1.1 (w/m2K), in
accordance with relevant British Standards (BS 6026: 1981) and current Building
Regulations (Approved Document L).
The structural elements of the entrance pod, door frames and window profiles shall be
grey. RAL 7024, powder coated to an 80% gloss finish.
The Contractor must ensure that the gable roof beam is not visible behind the front
windows. The beam must be hidden behind the Alucobond soffit.
In addition, the Main Contractor must not construct any columns behind the front glazed
windows.
The fixed glazing into the Sales area must have a window frame (F60 as per Building
Control requirements). The window must be one-way vision. Sills shall be laminated
chipboard (colour as per doors). Windows must be flush on the Sales area side. Fire
safety regulations must be adhered to.
The structural elements of the entrance pod, door frames and window profiles shall be
grey. RAL 7024, powder coated to an 30% gloss finish.
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 47 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
Corner protectors must be fitted to all exposed edges of the Entrance Pod.
The structural elements of the entrance pod, door frames and window profiles shall be LDID04
grey. RAL 7024, powder coated to an 30% gloss finish.
Entrance Pod Doors: 2 no. 1500mm doors from Pod to Sales Area.
1 no. 2000mm door from outside to Pod
The Principal Contractor must provide a mansafe area above the main entrance door.
Stainless steel ram protection is required from the end of the packing bench to the main
sliding door along the front elevation.
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 48 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
Consultant Construction (SCC). This item shall be manufactured in accordance with the
standard detail drawings. The cage door shall be equipped with fixed handles on both
sides. The following requirements must be met:
A double euro cylinder housing must be provided for to lock the door from both
sides.
The individual doors must be secured such that they cannot be lifted from their
guide rails.
The two sliding doors must be installed at a gradient such that they slide into the
open portion unaided when the lock is released.
When in the open position, the leafs must not project into the clear opening space,
in order to prevent accidental damage and bending.
The crash protection (100mm x 100mm x 6mm) at the floor must cover the entire
door leaf when opened. The crash protection must be fitted using 180mm heavy
duty anchors and also fitted with Dome Covers.
Bumpers to be installed to prevent wall damage by the sliding doors.
Suitable fixing area for IAS alarm contacts installed by others.
The Trolley Bay railings shall be manufactured from marine grade 316 Stainless Steel.
4 no. stainless steel, concrete-filled bollard are to be installed as ram protection, 1 no. to
each corner of the trolley bay.
A shelf with a depth of 300mm from the front edge of the window section, with a 10mm
void from the glass, is to be mounted at a height of 750mm. The Packing shelf must finish
950mm from the customer lobby wall, or 50mm past the door at full extension, to allow
the door to recess and also to prevent a customer from being struck while opening.
The shelf must be plastic coated, colour RAL 7024. Where the packing shelf abuts
adjoining surfaces it must be finished with a neat RAL 7024 grey mastic joint. The packing
shelf is to be installed modularly, so that it can be changed to suit the number of checkouts
set up at any time.
The 300mm wide melamine packing bench is to be fixed to the shop front mullion with
stainless steel brushed finished brackets. The bench top (colour RAL 7024) must have LDID04
round edges diameter 8mm on the top.
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 49 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 50 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
4.9 JOINERY
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 51 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
40mm black speckled granite worktop, with black silicone seal to wall tiles
Appliances to be supplied and integrated with white gloss doors (dishwasher,
refrigerator)
4.9.3 Mirrors
Mirrors must be fitted in the following locations using hidden fixtures: LDWA03
Male WC: 1 No. 700mm x 1000mm, above sink splash back, portrait style, upper LDWA04
edge 2,100mm above FFL. LDWA05
Baby Changing: 1 No. 700mm x 1000mm, above sink splash back, portrait style,
upper edge 2,100mm above FFL.
Customer WC: 1 No. 700mm x 1000mm, above sink splash back, portrait style,
upper edge 2,100mm above FFL.
Disabled WC Finger Basin: 1 No extra. 400mm x 1000mm, above sink splash
back, portrait style, upper edge 1900mm above FFL.
Disabled WC Standard Basin: 1 No. 700mm x 1000mm, portrait style, upper edge
1,900 mm above FFL.
Female & Disabled WC Finger Basin: 1 No extra. 400mm x 1000mm, above sink
splash back, portrait style, upper edge 1,900mm above FFL.
Female & Disabled WC Standard Basin: 1 No. 700mm x 1000mm, portrait style,
upper edge 1900 mm above FFL.
Male Locker Room: 1000mm x 2000mm
Female Locker Room: 1000mm x 2000mm
All WCs to be installed with sensor flush (flushing value of 4.5 litres or less). Where the
WCs are installed they shall have guidance or symbols instructing the user on the
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 52 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
appropriate operation of the flushing device. This shall be provided on the flushing
controls, or nearby for a group of cisterns if applicable. Geberit style frames and cisterns
must be used for all toilets.
The MC shall supply and install solenoid valves on the water supply to each toilet area in
the building to control the flow of water. The solenoid valves shall be linked to either;
Infra-red movement detectors within each toilet facility OR
Demountable panels rather than a tiled finish to be provided at the rear of all WCs.
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 53 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
b. Taps
Flow rate of each tap, at full flow rate in litres per minute at a dynamic pressure
of 3+ 0.2bar (3+ 0.02MPa) for high pressure (Type1) taps, or at a dynamic
pressure of 0.1+ 0.02bar (0.01+ 0.002MPa) for low pressure (Type 2) taps (BS
EN 200:2008, sanitary tap ware, single taps and combination taps for supply
systems of type 1 and 2. General technical specifications) including any
reductions achieved with flow restrictions.
d. Dishwashers
Litres/cycle
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 54 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
4.11.1 General
The works comprise the following:
Co-ordination, design and working drawings
Heating, Ventilation and Air conditioning of Store / Warehouse / Welfare block
Internal gas installation
Thermal insulation
Testing and commissioning
As-built documentation (including O&M manuals)
Installation Protocol
Store Opening Day: 1 hour response by heating and ventilation engineer
Store Opening Day: 1 hour response by electrician
Store Opening Day: 1 hour response by automatic door installer
The MC must allow for all design, supply, unloading, distribution, hoisting, placing and
fixing in position of all materials, plant and equipment, inclusive of the connecting, testing,
commissioning, balancing and handing over in working order to fully comply with Lidl
requirements and all current British Standards and Regulations.
The installation must be carried out by a Gas Safe registered installer (a gas certificate
must be provided by the MC as part of the as built manual).
Mechanical installations must comply with CIBSE.
Any scaffolding and platforms required for the installation of the works are to be included
for within the MC's works package.
Flues must be positioned on the roof on the side opposite to the car park.
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 55 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
All internal doors are to be fire-rated to the Fire Certificate requirements and must be
according to DIN 18360, BS 1245 and BS 1634-1 in both integrity and insulation.
All doors shall be fitted with doorstops. Finger protector strips must be installed on all
doors in UK.
The aluminium construction must be built with profiles in accordance with DIN 17611, and
the appropriate British Standards (BS 7036) in thermo-separated and thermo-insulated
construction to a U-value of entire construction as outlined in Section 1.2. No anodised
profiles are to be used.
All external steel doors and frames are to be Powder Coated RAL 7024 Grey on the
external and internal faces. The Entrance Pod, Automatic Doors, Front Glazing and
Window profiles shall all be powder coated RAL 7024 Grey on both faces. All powder
coating shall be to an 30% gloss finish. Refer to door schedule drawings.
All passive air vents are to be fitted with integrated ducts and intumescent grilles.
The MC must order, take delivery of and install ironmongery as indicated in the following
schedules. The ironmongery listed in Sections 5.6 and 5.8 is indicative of the items that
are to be installed.
5.2 MANIFESTATION
Where required by building control, manifestation should be applied to glazed screens LDSG01
and glass doors to avoid people being harmed by walking into them. In accordance with LDSG05
Building Regulations Part M, glass entrance doors and screens are clearly defined with
manifestation on the glass at two levels (850mm and 1500mm) above the floor.
Manifestation takes the form of a Lidl logo 50mm by 50mm spaced 300mm centres apart,
colour: frosted.
Openings for all external doors, windows, shop front, ventilation grilles, services intakes,
etc. shall be provided within the building shell in accordance with the standard Lidl details
and the site specific drawings to a tolerance of +/- 5mm. All structural openings shall
comply with the relevant Building Regulations. Attention is also drawn to the M&E section
of the Specification, where these works are described in more detail.
The Main Contractor must verify all builders works requirements with the Lidl
Refrigeration Installer prior to work commencing. All openings to be made good by the
Main Contractor on completion.
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 56 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
Thresholds at external door openings and the external paving/concrete shall finish 20mm
below the internal FFL level.
Structural Openings must be formed to cater for the requirements of the selected door
manufacturer in order to achieve clear finished openings as outlined in the table below:
Interior doors, which are not required to be executed as secure or FE doors (e.g. WC
doors), have to be constructed from powder coated light steel, colour grey (RAL 7024). LDDD01
Frames are to be galvanised steel frames as described above (with rubber seal) and LDDD02
should be powder-coated RAL 7024. Doors should be installed with ventilation grille LDDD03
(Utility Room) or with a door undercut (ca. 10mm above FFL). LDDD04
LDDD05
The door to the Managers Office needs to be equipped with door contacts which are to LDDD05
be connected to the IAS. When the door stands open for more than one minute during
the day an alarm needs to sound.
All doors with Maglocks shall have the Maglocks concealed within the door frame. No
wall mounted/visible fixtures to be installed.
Statutory signage must be supplied by the Main Contractor. All other signage to be
provided by Lidl UK GmbH.
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 57 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 58 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 59 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 60 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 61 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 62 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 63 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
For pest protection, all external doors and shutters shall not have gaps greater than 3mm.
All external doors have to be fitted with 3 pin locking system with a concealed rod within
the insulated door leaf and have to receive a 12.7mm floor mounted threshold and rubber LDDD01
lip, except the drivers door which is to be fitted with a retractable threshold seal. Drip-lip LDDD02
to be installed at the head of each door externally. LDDD03
LDDD04
Note: The 3-point locking is reset with master key and must be compatible with the panic LDDD05
bar fitted to fire escape doors. LDDD06
LDGF07
All exterior doors and the Cash Room and Managers Office door are equipped with alarm
contacts for connection to the intruder alarm system, factory-provided.
All external doors must be suitably reinforced at the head to facilitate the fitting of a
magnetic shear lock in accordance with the fire alarm system contractor.
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 64 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 65 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 66 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
The sectional door chain must be fitted to the floor at the side next to the drivers door.
Depending on the layout the chain must be tightened with a spring and fixed in the floor
slab. The sectional door must seal even to the floor when closed. Sufficient fixing points
for the installer to be provided.
The opening mechanism is to be completed with metal runs and to be equipped with an
automatic snap-lock system (internal locking/ unlocking only) a shootbolt operation on
one side, as well as manual reel chain with gear reduction.
The guide-rails of the sectional door have to be protected with ram protection bollards
from galvanised tubular steel, height ca. 300mm. The bollards are to be core drilled
recessed grouted into the concrete slab and must be painted with yellow and black stripes
at a 45 degree angle.
Complete wrap-around aluminium chequer plate protection should be fitted to protect the
wall opening reveals.
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 67 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 68 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
Note: Pole to operate the Mini Dock must be secured by a chain long enough to be fixed
to the internal dock wall where the pole needs to be stored when mini dock is not in use.
Sized at 2000mm wide x 535 550mm long x 500 550mm deep, max. projection 700
738mm. All dimensions depending on the supplier. The Mini Dock is to be fixed onto
the C section (cast into the concrete slab) via a continuous weld (continuous weld to
top for extra strength and stitch weld to underside). Welding certificate required.
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 69 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
Operators instructions to be fixed on the internal wall of the delivery pod. Steel wheel
guides, galvanised finish 170mm diameter with flared lead in 3050mm long, 323mm high,
including bolt down fix to concrete apron.
5.10 SALES / WAREHOUSE FLIP-FLAP (D09, D18, D35) F60 FIRE RATED DOOR
A flip flap door, or mid shop door, with vision panels must be fitted between the Sales
Area and the Warehouse. A concrete / steel frame is to be installed into the spine wall in
order to achieve a secure frame fixing. Clear dimensions of the structural door opening
are 1760mm wide and 2400mm high, with fittings and frame in RAL 7024. The door is
grey with a kick plate up to 1000mm from FFL. The vision panels are 200mm wide x
300mm high as per the standard detail drawings.
The frame of the flip-flap door must be fitted with ram protection bollards, consisting of
galvanised tubular steel (painted black and yellow at 45deg angle) on the Warehouse LDRL01
side and stainless steel finish on the Shop side, height ca. 300mm. Steels should be core LDDD03
drilled and grouted into the concrete slab. Stainless steel corner protection to be installed
on all three sides of the door surround (max. 80mm wide).
The cylinders will be delivered with 1 No. Master Key, which will provide the contractor
with access to all cylinders for the duration of the works.
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 70 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
Prior to Practical Completion the Lidl Senior Consultant Construction (SCC) will test the
door operation with the suited keys. The 1 No. Master Key must be returned to the Lidl
Senior Consultant Construction (SCC) at handover. Should this key not be returned,
the contractor, at no expense to Lidl, must replace the entire suited system.
Legend:
Code 1 Single cylinder
Code 2 Padlock, nominal 8mm shackle
Note: 2 Separate Masters to be provided. Yellow Master not to be suited to Red Master.
Red Master must operate Yellow Master suit (drivers door/drivers alarm box).
() = Optional
Yellow Master
Drivers Magnetic release 1No.
Suite 3 No. Key
Red Master Suite (5 No. Keys) (Roller Shutters Key Switch) (2 No.) If required
10 No.
TOTAL Cylinder
(4 No. Optional)
The clearance height and width of the single external sliding door openings is W 2000mm
x H 2125mm.
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 71 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
The sliding doors must be fitted with electronic sliding door drives (fixed in entrance lobby LDEP01
for outer drives, and fixed in Sales area for inner drives). Radar activation sensors and LDEP02
threshold safety sensors must be included, and a programme switch for each set of doors LDEP03
(operable without key) must be installed in the lockable programme switch box positioned LDDD01
internally adjacent to the lobby. Full height pocket screens must be installed to each set LDDD02
of doors. LDDD03
LDDD04
In accordance with the European Standards, the release radius of the sliding door radar LDDD05
sensors minimum 1000mm for entry and not less than 1500mm for exits. The so-called LDDD06
keep open period must be 0 seconds.
The door drives (including sliding door leaves and full height pocket screws eaves, with
programme switch and box) have to be bought from the relevant manufacturer as a
complete package, including assembly.
All sliding door leaves must be fitted with a brush strip each. Strips must not be face-
fixed.
Entrance / exit doors should be pre-fitted and pre-wired with suitable alarm contacts on
all doors ready for termination by the Intruder Alarm System (IAS) contractor.
The door installation contractor must supply cabling from the entrance and exit magnetic
contacts to the agreed termination point. This cable should be volt free, 4 cores. Cores
coloured Red, Black, Blue, and Yellow. Red and Black provide Tamper. Blue and Yellow
provide Circuit. The intruder alarm contractor will then provide a junction box and connect
to this cable.
Doors must be programmed to open upon failure of power supply (except when intruder
alarm has been set). Liaison is required with the Fire Alarm contractor to ensure that
doors are correctly wired into the relays open upon activation of the fire alarm.
Both the Door Contractor and the Alarm Contractor must be on site to test the alarm
system on completion of the installation.
Fittings external door: For opening purposes, the outer door must be fitted with a key LDEP01
switch, flush to profile with tamper-proof fixings. The switch should be inserted into the LDEP02
corner bead of the entrance porch from the outside. LDEP03
Fittings internal exit door: The activation unit for the IAS (provided by IAS contractor)
and door release button (provided by Auto Door Contractor) must be installed in the exit
lobby.
Fittings internal entrance doors: No key switches or release buttons should be installed
for the internal entrance doors. They are operated via a programme switch.
Entering the Store: By operating the external key switch, the external exit door will open
and automatically close again after the lobby has been entered. By deactivating the
Intruder Alarm System (IAS) via the activation unit, the release button will be energised
for unlocking the inner exit door. By operating the release button, the inner exit door will
open. At the start of trading hours, all programme switches have to be switched to day
operation / automatic.
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 72 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
Leaving the store: Before leaving the store, all programme switches for the sliding doors
must be set to off (locking) in the programme switch box (RAL 7024). The release button
to open the internal exit door (positioned on the Sales area side) will be energised.
After entering the lobby and allowing the internal exit door to automatically close and lock,
the activation of the IAS can be triggered. In setting the alarm, the release button (located
in the lobby) for opening the external exit door will then be energised. After the manager
leaves the lobby, the external exit door will automatically close and lock. The assembly
company must instruct the Lidl Senior Consultant Construction (SCC) in the operation of
all doors prior to leaving site.
All door controls located in the grey lockable box must be labelled on completion so that
each control is marked up to correspond with the relevant set of doors.
Three No. powder coated grey RAL 7024 glazed aluminium double-leaf doors shall be
installed in the Entrance pod. All doors are to have proprietary brush seals positioned
along the bottom edge of each door to prevent leaves and vermin from entering the lobby.
Each door leaf shall be single glazed using laminated safety glass incorporating an acid
etched British Standard safety mark.
Automatic doors must comply with BS 7036 code of practice for installation and operation.
Automatic electro-mechanical sliding door operator control equipment with integral PCB
incorporating timer relay adjustable from 0-30 seconds shall be installed to the entrance
/ exit doors as follows:
Insofar as is permissible by regulations, the activation radius of the sliding door
radar sensors is approx. 1200mm in front of the particular sliding door and the so
called hold open time is 0 sec.
3 No. overhead mounted radar / infrared movement detectors with fully adjustable
detection range (above outer & inner entry and exit doors).
Overhead infrared surface mounted impulse safety units OR mid-rail infrared flush
/ surface mounted impulse safety units to both sides of all doors.
Extruded rubber finger guards and fixing bar to doorjambs where necessary.
1 No. momentary key-switch located at the outside of the exit doors. The
momentary is achieved by way of key box fitted with a single Europrofile housing
recessed into the Pod frame at the car park side of the exit doors (picture below).
2 No. push buttons on the internal side of the exit doors to allow entry / exit from
the store when the automatic doors are switched off.
3 No. thumb-turn switches (not keys) to be located in the Managers Office (one
for each door) to allow for control of the doors via a 4-position switch. Six-core
standard alarm cable to be provided and brought from the Automatic Doors to the
office switches.
3-point mechanical locking mechanism on master suite to be provided to the outer
exit/entrance door.
The aforementioned thumb-turn switches in the Managers Office must be clearly
and durably labelled.
Finish to radar units, mid-rail cover and all other visible parts shall be powder
coated grey RAL 7024.
Each door leaf is to incorporate a fail open device to open the doors in case of
power failure. This is to conform to BS 5588 Amendment No. 2. This feature must
be bypassed when the intruder alarm is armed to prevent would-be intruders from
cutting the power to gain access to the store.
The door control specialist shall liaise with the Lidl direct Fire Alarm Installer to
ensure that all automatic doors release to the open position in the event of a fire.
The door control specialist shall ensure that all final connections have been made.
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 73 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
5.13 SECURITY
The MC must liaise with Lidls IAS installer to ensure all electrical connections are
completed.
The MC must liaise with Lidl IAS installer to ensure all electrical connections are
completed.
The Main Contractor must allow for all BWIC (builders works) in the services installation.
Fire extinguisher locations must be agreed at planning stage. The Main Contractor must
obtain all relevant fire strategy drawings from the Lidl Senior Consultant Construction
(SCC) prior to commencement of the works.
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 74 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
Should the finish be unacceptable to the Lidl Senior Consultant Construction (SCC), the
flank wall of the staircase must be plastered to an acceptable level at no to cost to Lidl
UK GmbH. The landing at the head of the stair must be laid to falls.
5.18 WINDOWS
LDSG05
5.18.1 Window Measurements
The window mentions and sill heights are as follows:
Clear Opening (mm) Sill level from FFL
Area
Width Height (mm)
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 75 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
Front Glazing and Window profiles shall all be powder coated RAL 7024 Grey on both
faces. All powder coating shall be to an 30% gloss finish.
The full height glazed shop front must to be installed to the gable side and one adjacent
to the lobby/entrance door, the shop front must be designed in consideration of structural
requirements for the overall surrounding structure.
LDEL01
All glazing panels have to be double-glazed, with laminated safety glass, 8.8 / 16 / min LDEL02
8.8mm glass unit voids to be argon filled. Inner pane to have a low-E soft coat to face LDEL03
three in accordance with relevant British Standards (BS 6026) and current building LDEL04
regulations (Approved Document L). No units of the shop front should be openable. LDEL05
LDEL06
The windows and curtain walling profiles and glass panels can require a F60 rating for LDEL07
the shop front depending on the regulations. LDEL08
LDCD02
The F60 fire-rated window system is required to the main (curtain wall) front window if it LDSG01
LDSG02
is 15m or less from the boundary or centre line of the road. The exact minimum
LDSG03
dimensions required from a boundary wall depend on the particular constraints.
LDSG04
Therefore the calculation for minimum distance from a boundary must be performed for
LDSG05
each individual site at pre-construction stage.
The glass openings at the gable side to be planned with 16 panels (18 panels for a shop LDSG02
front length of 25.50m), widths will vary from 1953mm to 2241mm and up to a maximum
height of 7.0m above FFL.
The Contractor must ensure that the gable roof beam is not visible behind the front
windows. The beam must be hidden behind the Alucobond soffit.
The Main Contractor must co-ordinate lobby, autodoor and floor tiling installers in order
to set out the correct threshold position.
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 76 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
fixed at a height of 720mm from FFL to the underside of the PVC skirting. Corner
protection supplied by Rockling Plastics refer to Suppliers Schedule for contact details.
Inner pane to have a low-E soft coat to face three to achieve the required U-value in
accordance with relevant British Standards (BS6026) and current building regulations
(Approved document L).
The internal window sill should be tiled using the grey floor tiles, with the joints between
the tiled shelf and wall sealed using white mastic joint sealant.
Exterior window sills are covered with a powder coated aluminium sheet (2mm) with
sufficient projection and raised edges on the side. Colour: grey RAL 7024.
Windows to the Canteen, Office and Stairwell must be openable. They must be hinged
at the bottom and open inwards. The window in the stairwell must be fire rated to comply
with the rating of the fire compartment / protected stairwell.
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 77 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
6.1 GENERAL
The sub-base together with the road and paving build-ups must be designed to suit the
engineering requirements of all the specific site conditions. All materials and methodology
used must be approved in writing by the Lidl Senior Consultant Construction (SCC).
The entire hard landscaped area, estate roads and car parking spaces have to be
constructed for HGV/44t in accordance with the geotechnical report plus BS: 7533-1,
7533-2 & 7533-3 in respect of block paved construction and BS EN 13108-1 Asphalt
Concrete, BS EN 13108-5 Stone Mastic Asphalt & BS 594987 in respect of bituminous
pavement construction. The compaction of the sub base must be proved by plate load
tests during the works in co-operation with the Lidl Senior Consultant Construction (SCC).
The Lidl Senior Consultant Construction (SCC) must be in attendance when the
tests are taken.
PMB Polymer Modified Bitumen must be used in HGV routes and heavily trafficked
areas.
Before starting the work, a pavement plan must be submitted and approved by Lidl Senior
Consultant Construction (SCC).
The clearance width of the estate roads between the car park rows must be between
6500mm and 7500mm. The width of entrance and exit 9000mm.
Note: No driving directional arrows are to be marked in the car park, the only exception
where one way system. No white lining on key block paving to be used, parking spaces
are (only marked on the asphalt) with a permanent two-component cold plastic in the
colour White
6.1.2 Gradients
Gradients to car parking areas are to be between 1% and 2% and must always fall away
from the store. Gradients to access routes into the site are not to exceed 5%. Any
deviation from these fundamental rules must be approved by the Lidl Senior Consultant
Construction (SCC) in writing.
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 78 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
Car parking spaces shall be 2.5m x 5.0m (2.5m as measured from centre-to-centre of
dividing lines). If the spaces overhang a landscaped area, then they must be reduced to
2.5m x 4.7m.
Disabled parking spaces are to be provided in line with the conditions of the Building
Regulations, with a minimum of 4 No. required. Overall width 3.60m, includes a 2.40m
car parking space. A 1.20m clear way of hatched yellow to be painted to the RIGHT and
REAR of the space. A disabled symbol in yellow block paviours is required for all disabled
spaces. The location of the disabled parking spaces will be agreed in writing with the Lidl
Senior Consultant Construction (SCC) and dimensions and layouts can be found on the
detailed drawings.
A Minimum of 3 No. Parent & Child car spaces must be provided. Overall width 3.60m,
includes a 2.40m car parking space to be painted and a 1.20m clear way of hatched white
to be painted to the RIGHT and REAR of the space. A Parent & Child symbol comprising
white painted paviours is required. These P&C spaces are to be located in the spaces
immediately in front of the Entrance doors. Exact location to be agreed in writing with the
Lidl Senior Consultant Construction (SCC).
All routes around the car park must be Min 6.5m 7.5m wide. Access and egress routes
to the site must be 9.0m wide.
If there is a bank of more than 8 No. spaces immediately in front of the entrance canopy
then a pedestrian walkway must be incorporated to provide access through the spaces
to the store entrance. Pedestrian walkways should be marked with a running man
symbol.
If there are lighting lamp posts within the car park (which should be avoided where
possible), the lamp post must be centred in a bank of 4 car parking spaces. The finish
around the base of the lamp post protection to be a concrete square, coloured to match
block paving. Lamp posts in areas of low impact risk are to be protected with galvanised
hoops as per the standard detail drawings. Lamp posts more than 750mm behind the line
of kerbing in the landscaping area do not require protection. Lamp posts that stand a high
risk of vehicle impact are to be protected using larger galvanised hoop protectors. This
must be agreed in writing by the Lidl Senior Consultant Construction (SCC).
Attenuation tanks and oil interceptors are to be installed in as required by the local
authorities or the relevant planning permission bodies. Their location is to be agreed in
writing with the Lidl Senior Consultant Construction (SCC)
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 79 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
Disabled car spaces (number in to be agreed with Lidl Senior Consultant Construction LDSP01
(SCC)) must be installed in accordance with Approved Document M to the measurements LDED02
in the table above.
Disabled spaces are to be located near the store entrance and be moved forward into the
soft landscaping area so as not to encroach on the estate roads.
The quantity of disabled spaces must also comply with the requirements of the local
development or Local Area Plans.
Parking bays have to be constructed with block paviours (200 x 100 x 80mm) with
bevelled edges (no grass pavers!). Estate roads have to be constructed bituminous
pavement construction with a 0/10mm stone mastic asphalt surface course.
In Scotland and where soak away drainage is required parking bays must be constructed
using Marshalls Aqua Priora drainage paviours.
Flush kerbs must be installed between parking spaces and estate roads Size 125 x
255mm Type CS1 to BS EN 1340.
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 80 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
Note: For cutting and trimming blocks and kerbs, Guillotine cutter must not be used.
In the area of the building perimeter, parking spaces, and the shop front windows, a guard
board with 300 x 300mm flagstones, 900mm wide and with Type HB2 kerbs (125 x
255mm to BS EN 1340) laid with a 100mm kerb up stand have to be provided as ram
protection for the building. The contouring of the paved areas to the green areas is
defined by upstanding kerbs, external corners are made of rounded shaped kerbs.
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 81 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
The area of the entrance must be constructed with 125 x 255mm Type CS1 kerbs to BS
EN 1340 laid flush with the adjoining areas. In the area of the customer entrance, the
paving stones have to be laid in such a way that there are no cut-to-size paving stones
at the transition to the lobby threshold.
Soft landscaped areas, which have been determined by the authorities, must be planted,
provided no other regulations exist, with easy-care ground covering plants (e.g. ivy,
cotoneaster, potentilla yellow, spiraea bumalda), plant height ca. 300mm, with min. 5
branches, plant density 7 plants/m.
Any trees must have a trunk circumference 160-180mm at the time of planting. Easy-care
varieties such as maples or elms have to be planted (no lime trees, birch trees, poplars
or conifers).
In between the topsoil and bark mulch there must be a geotextile membrane with min.
200mm overlap and holes cut for planting. Sufficient pegs to be installed to prevent
membrane from lifting.
Consideration should be given to sloping landscaping where the bark mulch will slide
down the membrane. In such instances the MC is responsible for finding a solution to
retain the mulch in place.
The MC is responsible for maintaining the hard and soft landscaping for a period of 12
months following practical completion.
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 82 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 83 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
bitumen (PMB) tarmac. HGV route to be agreed with the Lidl Senior Consultant
Construction (SCC) prior to installation.
Pitch jointing applied to SMA should generally not be required, but in instances where it
is required, the agreement of the Lidl Senior Consultant Construction (SCC) should be
obtained in writing prior to commencing and it must be laid in straight lines with a line
marking shoe to maximum 50mm thickness.
The wearing course must be presented at Practical Completion in perfect condition.
Localised patch repairs are not permitted. If a repair is required, the full section must be
replaced. All repairs must be agreed in writing by the Lidl Senior Consultant Construction
(SCC).
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 84 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
If deemed necessary by the structural engineer, a soil sterilisation technique may need
to be carried out e.g. geotextile membrane. This solution must be approved in writing by
the Lidl Senior Consultant Construction (SCC).
Paver Joints
The jointing material must be made of recycled mix, granulation 1 3mm with part of
fine grit.
Must not be able to filter through the Paver Sub Base (D15/d15 1; D15/d85 4; D50/d50
5).
Jointing material must be swept into the joints and compacted with a concrete vibrating
unit with rubber plate.
The pavers must be compacted until completely flush.
The pavers must not be cleaned with a vacuum sweeping machine.
6.4 KERBING
Pre-cast concrete Trief kerb is to be laid at the corner of and down the length of the
delivery ramp to protect both the corner of the building and the projecting eaves from
potential impact damage by HGVs. The final kerb at the upper end of the ramp and at the
drivers stair is to be chamfered so as to finish flush with the standard kerb level.
Precast flattop edging kerbs, 125mm wide, butt-jointed finishing flush with adjoining
surfaces must be used to set out and delineate between:
Access routes and car parking spaces
Trolley bay and adjoining surfaces
300mm x 300mm Quadrant Kerbs must be used where kerbing meets at a 90 angle.
Corner kerbing must not be cast in-situ. Regular kerbs must not be cut and butt-
jointed at 90 angles.
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 85 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
to maximise aisle width. The paving should be 300mm x 300mm, square charcoal
coloured pavers, laid in a stretcher bond pattern and on a semi-dry lean concrete mix
bedding mortar. Pavers should be installed as per the drawing detail. In front of the side
fire exit door(s), the surface of the walkway shall be 20mm lower than the FFL of the
Sales area, in order to form a barrier to prevent rainwater ingress.
The fire escape footpath to the rear of the store must have a clear width of 1800mm for
a LOF 14 and 2300mm for a LOF 17.
SW and FW drainage chambers should not be located at the head of the goods delivery
ramp. Where possible, these should be offset from the head of the ramp to avoid constant
trafficking over these (HGV rated chambers / covers).
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 86 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
At the top of the ramp at the junction between the concrete and asphalt traffic lane, any
damage to the concrete edge must be avoided. All damaged concrete must be repaired
prior to installation of the asphalt car park layer.
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 87 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
Directional arrows are only to be used in car parks where a one-way system is in
operation and only on approval in writing by the Lidl Senior Consultant Construction
(SCC).
The arrangement, design and the amount of external lampposts shall be established in
Light Level calculations to be provided by the approved Car Park Lighting Supplier and
agreed in writing with the Lidl Senior Consultant Construction (SCC). A minimum lux level
of Em=10 lux and a uniformity level of 0.25 shall be achieved. The height of the light heads
of the car park lighting is 6.00m.
A lux sensor shall be mounted on the building to control the external lighting scheme
including signage. The position of the sensor will be site specific but will generally be
located on a north-facing wall. Exact positioning is to be advised by the BMS
subcontractor before commencing construction. A cage is to be provided to protect the
sensor.
Appropriate lighting is to be installed at the backside of the building leading to the Utility
Room, including a motion detector. (7 lux to be achieved). A cage to be provided to
protect the sensor.
The Lidl Senior Consultant Construction (SCC) will order the external signage, and it is
the Contractors responsibility to accept delivery and store the signage safely until it is
installed. The location of the pylon and building signs must be agreed in writing with the
Lidl Senior Consultant Construction (SCC).
A concrete foundation for the external pylon sign shall be formed complete with bolt cage,
with site specific foundation design prepared taking into account geographical variations
for wind loads, soil conditions, etc.
For all illuminated signage an independent 5A / 230V / 60Hz single-phase supply shall
be taken through a duct to the signage and connected.
Signage will be provided free issue by Lidl UK GmbH and the installation and location
must be agreed with the Lidl SCC.
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 88 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 89 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
The edge steel profile bead at the Mini dock edge must be painted with black and yellow
stripes at an angle of 45.
Concrete filled stainless steel bollards are not required if the width of the footpath is
greater than 1m wide.
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 90 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
A 2.0m high paladine fence (RAL 7037) must be installed to fully secure the condenser
compound area. The location of this compound should be approved in writing with the
Lidl Senior Consultant Construction (SCC). The fence should be secured using posts at
2,515m centres with 2,500m panels of 50 x 50 x 4.0 SHS galvanised and butt welded at
the corners. A lockable pedestrian gate must also be installed to allow access and be
included on the master suite.
The MC must prepare design drawings illustrating the vulnerable areas / parts of the
building and the durability measures specified.
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 91 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
The direction arrows are to be positioned as per advice from the Lidl Senior Consultant
Construction (SCC), and to be set in concrete to a height of 1200mm (upper edge pipe)
above ground level.
Special attention is to be given to the fact that all signage does not pose a line-of-sight
obstruction when exiting the parking area.
For the setting up of lighting columns, grounds sleeves (DN 400) including electrical
wiring are to be set in concrete at the planned column locations. The sleeves are filled
with sand and a 100mm thick concrete seal is applied as closure and for fixation of the
lighting columns. Lighting columns at risk of being struck by traffic are to be protected
with a galvanised impact barrier.
A safety railing must be provided along the edge of any retaining walls on the delivery
ramp. This should be formed from galvanised steel tubing at a height of 1100mm
minimum for fall protection with one intermediate rail with vertical rails at 1.5m centre.
Refer to the standard drawing detail for fixings to the RC wall.
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 92 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
The trolley bay to be fixed with concrete foundations prior to laying of block paving. A
drainage outlet must be provided for the roof water to drain to the surface water system.
One pylon sign at the approach of the main property or at a highly prominent location
near the property, in addition two gable signs on the new glazed frontage design, and a
Lidl Non-Food display cabinet have to be installed in agreement with Lidl (MC to allow for
electrical power supply).
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 93 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
For the installation of the pylon sign, a concrete base with root cage in accordance with
manufacturers instructions must be installed by the MC before the signage is delivered.
(Lidl to order and supply anchor basket with the corporate signage)
Where the existence of a car park is not visible from the street a sign supplied by Lidl
stating Customer Car Park to Rear of Store must be installed by the MC.
Note: Pylon sign supplied free issue by Lidl. The bolt cage is to be provided in advance
so that the foundation canbe installed in advance of the sign arriving on site.
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 94 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 95 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
7.0 SERVICES
The regional property office obtains fixed quotations and pays for the statutory services.
Lidl are responsible for obtaining provisional installation dates for the statutory services.
The contractor is responsible for providing any necessary trenches, ducts, chambers,
pits, holes, etc. for services within the site boundary, and must liaise closely with Lidl and
the utility companies with regard to dates and final connections. The Main Contractor is
to contact, program and agree fixed dates with each utility provider.
7.1 DRAINAGE
Separate foul and surface water drainage systems shall be provided and connected to
the main public sewers. All necessary manholes, inspection chambers and rodding points
shall be designed and constructed in compliance with the detailed requirements of the
Planning Permission, the Building Regulations and the standard details as attached.
Drainage runs and layouts shall be designed in accordance with BS8301 and shall permit
easy access for maintenance to all items of drainage both below and above ground.
All gullies must be accessible for cleaning and must have a trap bucket inside of it for
removal of rubbish and other potential drain blocking materials. Gullies must be formed
using standard gully pots. Block / brick built gullies are not permitted. All manhole
coverings and gullies are to be installed to DIN EN 1433 Class E600 (600KN). Manhole
covers must be protected when asphalting. The gullies are to be ideally located around
the perimeter of the car park or in the middle of back to back car parking spaces.
Foul and surface water drainage pipe runs underneath the building shall be kept to a
minimum. All drains must be suitably trapped to prevent foul air and smells entering the
building. No manholes within the building are permitted without written permission from
the Lidl Senior Consultant Construction (SCC). All chiller and sluice drainage pipes shall
be at least 100mm diameter. The condensate drains are to be equipped with rubber
flanges which are to be located flush with the floor tiles. The location of these is to be
agreed in writing with the Lidl Senior Consultant Construction (SCC).
All foul and surface water drainage pipe runs shall be accessible for rodding. Upon
completion, the contractor shall provide the Lidl Senior Consultant Construction (SCC)
with a CCTV inspection of all drain runs to show that they are free of obstructions. A
copy of this summary must be included in the O&M manuals.
If required by the Planning Permission, a retention tank and oil interceptor must be
provided to collect and filter the surface water drainage prior to discharge to the public or
natural drainage system.
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 96 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
falls within the curtilage of the site, the responsibility for organising this connection
remains with the MC.
It is critical that the installation of the foul drainage is laid 100% in accordance with
Building Regulations and British Standards, planning consent requirements, Water
Authority requirements and the tender documentation. The foul water drainage layout
shall be agreed in advance with the Project Engineer and Lidl Senior Consultant
Construction (SCC). It is the MCs responsibility to contact the Approved Inspector
(Approved Design) or the Local Authority Building Control Officer in Scotland in advance
to arrange for the trench, bedding, and pipe installation to be inspected prior to it being
backfilled. An air-pressure test should be undertaken before and after backfilling works
to ensure that the pipework has not moved or been damaged. It is critical that all pipework
is tested and confirmed as acceptable prior to any building works being undertaken above
the pipe run.
Upon completion of the sanitary installation, the foul pipework system below the floor slab
in each area of the store (inclusive of the chiller condensate drainage) requires to be
pressure tested. Each area should be isolated at the relevant manholes, with a successful
pressure test demonstrated to the Lidl Senior Consultant Construction (SCC) and
Building Inspector. The company undertaking the pressure test must provide a signed
report upon completion, which should be issued to the Lidl Senior Consultant
Construction (SCC).
In Scotland a completion certificate for the store will not be issued by the Local Authority
Building Control Department unless a successful pressure test of the completed system
(inclusive of all sanitary fittings) has been demonstrated to the Building Control Officer.
As installed drawings and a CCTV survey report of the full installation are required upon
completion and referenced in a specific section of the O&M file.
As installed drawings and a CCTV survey and report of the full installation are required
upon completion and referenced in a specific section of the O&M file.
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 97 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
Downpipes on any elevation facing the car-park have to be circular vandal proof / heavy
duty galvanised steel pipes, ca. 3mm thick, up to a height of 1500mm (Loro-X) with
access panels in the lower section.
All rainwater downpipes to be securely anchored to the building with tamper-proof fixings,
and provided with low level rodding points or inspection covers on every rainwater
downpipe.
All separate condensate drains have to be put together in one main drainage run. Both
main drains have to end in a chamber, closed with a manhole outside the building and a
tiled rodding chamber on the opposite end of the line.
All below-slab drainage must be fully air pressure tested prior to the building slab being
poured and once the refrigerator cabinets have been installed.
In accordance with the refrigeration company resp. Lidl, floor gullies measuring DN
100mm in diameter with a DN 50mm reducer, have to be installed for the chiller
condensate drainage. Odour traps must be installed, with stainless steel gully gratings
and a 50mm reducer.
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 98 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
The parking area drainage and gradient design for paved areas are to be in
accordance with technical and economical parameters. The slope is to be designed away
from the building, (except delivery ramp) with a gradient of max. 2.0% and must not fall
below 1%.
Only if required, a concrete slot channel can be built at the entrance and exit to the parking
area, between parking area and public walkway. The gratings for the gullies are close-
meshed up to 16mm. The drains are to be positioned at the edge of the boundaries or
grassed areas as well as in the crossover point of the parking spaces in case of double
parking space rows. After completion, the ground pipes are to be cleaned with a high
pressure cleaner. Solids are to be removed.
The car park gullies are to be positioned around the car-park boundaries, and in the
middle of two adjacent (or opposed) car parks. Gullies are class D400 (BS EN 124), kerb
hinged opening with mesh grating and leaf bucket, Code DU 5801M by Durey Castings.
There are to be no drainage gullies located in or at the joints between parking bays/estate
roads.
The lowest point of the delivery ramp must be drained by a heavy load drainage channel
positioned approx. 40 cm in front of the ramp wall. Back fall to be created from the face
of the ramp wall into the drainage channel.
7.2 DUCTING
Ductwork generally shall be laid on a bed of sand and covered with pea shingle. All bends
shall be long radius type with access points at regular intervals. Draw ropes must be fitted
in all ducts.
The ducting must be between 100-200mm underground across the entrance area.
Installation of the system will be by the Lidl direct sub-contractor.
After installation, ducts shall be plugged to prevent ingress of rubbish and soil. After
cables have been pulled, the ends of the ducts shall be sealed to prevent ingress of
vermin and water.
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 99 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
1 No. 100mm uPVC duct terminating flush with FFL in utility room (Car Park
Lighting)
A floor channel will be constructed under the tills at a distance of 2.950m from the front
windows. Two 150mm diameter ducts for data cables must be formed in a closed floor
channel. The channel will link the tills area to the IT Room on the first floor.
One 150mm diameter power duct will be required from the Cash Room to the tills area.
This can be formed with a deepening in the concrete floor. Three 70mm diameter ducts
are required at various locations in the Sales Area floor. These ducts can be formed with
a deepening in the concrete floor.
Duct chambers will be connected together on the Sales floor via 2 No. 70mm diameter
duct pipes. All pipework and duct chambers must be locataed under shelves.
The exact location and specification of the service route should be agreed following a site
meeting with a representative of the BT and the Lidl Senior Consultant Construction
(SCC). Meeting to be arranged by the MCs site agent; contact details and site specific
site reference number are to be provided by the Lidl Senior Consultant Construction
(SCC) at the pre-start meeting. On site meeting to take place no later than week 2 of the
contract.
All ducts are to be concealed. The Secure box which covers the Distribution Point will be
provided free issue to the MC by the Lidl Senior Consultant Construction (SCC).
The MC should include for 1 No. BT chamber / manhole within the Lidl site boundary to
allow for a change in direction within the site. Specification for chamber to be as per
standard BT requirements for a footway/carriageway box with all necessary entry / exit
ducts.
All service penetrations through the floor (or occasionally through the walls or fire rated
ceiling) must be suitably sealed upon completion. A gas seal will be provided by BT. the
MC should check that this has been installed (where the duct enters the Utility Room
floor) prior to the BT engineer leaving site.
It is possible that different engineers install the ISDN & PSTN lines and the DP. The MC
is responsible for liaising with the BT engineer when he arrives on site to ensure that the
PSTN & ISDN lines are installed in the correct location within the lockable box.
Note: The SCC is to raise an order with Gamma so that site specific lines can be installed.
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 100 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
It is the responsibility of the MC to contact the gas service provider to arrange suitable
program dates for the installation of the service to ensure the mechanical installation is
fully operational for PC. It is important that the MC gives the gas service provider
adequate notice prior to the proposed installation date. The MC must also arrange for the
gas service providers inspection engineer to undertake a trench inspection prior to the
installation date in order to ensure that the trench and all other civils works on site are
accepted by them.
It is the MCs responsibility to ensure that the full internal / external gas installation back
to the meter is installed by a registered Gas-Safe engineer. The MC must provide a Gas
Safe certificate upon completion of the installation. (Must be provided at least 1 week
prior to PC in Scotland).
Note that the gas provider may install the meter within a boundary box on the site
boundary (exact location of this to be agreed with the Lidl Senior Consultant Construction
(SCC)). In such cases, the MC is responsible for providing a concrete base for the box,
and any supply pipework leading into the Utility Room. This pipework must again be
installed and certified by a registered Gas-Safe engineer. If the meter is to be installed
internally, it should be positioned within the Utility Room. The gas service provider will
mount the meter on a shelf no more than 1700mm from FFL.
Under no circumstances should any gas pipes pass below the store.
7.4 WATER
It is the responsibility of the MC to contact the water authority to arrange suitable program
dates for the installation of the service to ensure the mechanical installation is fully
operational for PC. It is important that the MC gives the water authority adequate notice
prior to the proposed installation date. The water meter will generally be installed on the
site boundary, with the contractor responsible for the installation of the pipework from the
meter to the Utility Room, the meter chamber and double check valve on the site
boundary. The MC must also arrange for the water authority to undertake a trench
inspection prior to the on-site pipe installation date in order to ensure that the trench and
all other civils works on site are acceptable to them.
Once the supply pipe has been installed, it must be pressure tested and chlorinated prior
to the final connection being made. The MC is responsible for arranging for the necessary
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 101 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
testing of all water supply pipework installed within the site. Upon receipt, the MC must
immediately issue the chlorination /pressure test results to the water authority, who will
then make the final connection within 14 days (subject to agreement of test results). If for
any reason the final inspection is not made within this timescale, the pipework will have
to be re-chlorinated at no cost to Lidl.
On sites where contamination has been identified within the site investigation report, the
MC should allow for the supply and installation of copper or specific contamination-
resistant barrier pipework. Refer to Site Investigation Report for confirmation of suitable
material for the water supply pipework.
If a fire hydrant is required within the site, the MC must appoint a suitably qualified sub-
contractor follow the above procedures for the supply of water pipes and must also lay
suitably sized (usually 90mm) pipes for the hydrant connection. A specialist company will
be required to install the hydrant themselves, together with the suitable pressure-resistant
pipework. As with the water supply, the hydrant supply must be pressure tested prior to
connection, in addition to the chlorination test detailed above.
The MC must fully comply with the local water authority by-laws; a final inspection of the
completed internal installation (including sanitary ware) will often be required prior to the
water supply being turned on. Water bye-laws certificate to be issued to Lidl on PC.
Note MC is required to pay for their water usage during construction works; in areas
where the water is chargeable, if an existing metered supply is to be used for temporary
building water, Lidl will provide details of the amount consumed during the project and
deduct the water usage charge from the MCs final account.
7.5 ELECTRICITY
The Utility Room must be watertight with a lockable door prior to the electrical supply
authority commencing their works. After the room is rendered a plywood board must be
installed on the Utility Room wall for the electrical company to fix their equipment onto.
The local network provider is responsible for laying the cable within the trench, and
feeding this into the Utility Room via the duct (EATS 24 compliant black rigi-duct) installed
a suitably sized switched fuse and tails within the floor (by the MC). It is the MCs
responsibility to make arrangements to install the cable-head and CT panel onto the
plywood backing panel mounted on the wall.
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 102 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
Note: The network provider may not be obliged to carry out any works if there is
scaffolding on the building, particularly in the vicinity of the Utility Room. It is the
responsibility of the MC to ensure that this does not lead to delays.
It is the MCs responsibility to install the mains-switch and earth-bar within the Utility
Room. This should be installed adjacent to the proposed cable-head location, prior to the
electrical supply authority arriving on site to commence works. The Lidl approved mains
switch must be installed by a NICEIC approved contractor, with an installation certificate
available on site. It is the responsibility of the MC to ensure that the mains switch and
tails are designed and sized to suit the capacity of the electrical supply for the store.
The electrical meter is generally installed at a later date, and by a different company from
that which installs the cable-head. The Lidl Senior Consultant Construction (SCC) is
responsible for applying for the electrical meter, and will provide the MC with the contact
details so that they can arrange the meter installation date.
Note it can take 3 weeks or more for the meter to be installed by Lidls electrical shipper.
Once the Electrical Supply Authority have confirmed the date for cablehead installation,
the meter installation should be requested for the following day. A return visit by the
Electrical Distribution Company may be required to energise the supply after the meter is
fitted.
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 103 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
8.1 LABOUR
Only fully qualified and competent tradesmen, together with their necessary labourers or
helpers will be employed by the Contractor on the works. The Contractor will provide full
and adequate supervision and site administration during the progress of the works and
will keep a competent and authorised Agent or General Foreman, approved by Lidl,
constantly on the works. Such authorised Agent or General Foreman will give his whole
time to the supervision of the works and must be able to receive and act upon (on behalf
of the Contractor) all instructions, directions or orders issued by Lidl.
8.3 QUALITY
The Contractor will fully comply with the documentation provided by Lidl and its appointed
M+E Consultants and all current Scottish or British Standards and Regulations, and Good
Working Practices.
8.4 INSURANCES
The Contractor will retain on site all necessary insurances as required by the Contract
Documents.
8.5 INSTRUCTION
The Contractor will instruct Lidl staff in the operation and maintenance of the various
components forming the installation. The Contractor will prepare maintenance and
operational manuals as set out later in this Specification.
8.6 INSPECTION
The Contractor will, before covering up any work, give Lidl reasonable opportunity to
inspect the works already executed. The Contractor will give all such notices and provide
such facilities as may be required to Statutory Undertakings, entitled to carry out
inspection, or examination of the works or part of the works. The Contractor will not
interfere with, or disconnect or remove any existing services without prior arrangement
and without prior agreement.
8.8 SECURITY
The Contractor will comply with all security requirements as detailed in the Contract
documents.
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 104 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
8.9 WARRANTIES
The Contractor will include cost for 1 year warranties on all equipment.
8.12 LABELLING
All equipment, be it mechanical, heating or electrical equipment, or even equipment
provided by Lidl Direct Trade Contractors, will be durably labelled using engraved labels
and the appropriate label holder, e.g. isolator switches, pod door controllers (office),
pumps, heating circuits, boilers, sub-distribution boards, etc.
The Contractor will include for providing heat sealed schematic layouts framed and
located within each of the utility rooms.
8.13 TESTING
All testing and commissioning, balancing and handing over in working order will also be
included.
8.14 MEETINGS
The Contractor is to include for all necessary meetings, reviews, co-ordination and
integration necessary for the design, installation and completion of the project.
8.15 CO-ORDINATION
The Contractor will lead co-ordination of the building services installation. The Contractor
will lead and co-ordinate the production of all building services drawings including
services provided by Lidl Direct Trade Contractors (this includes Refrigeration, Fire
Alarm, Intruder Alarm and CCTV).
The Contractor needs to co-ordinate the final routes of all distribution systems (including
those installed by Lidl Direct Trade Contractors) and will ensure there is no conflict of
routes or services or conflicts in the drawings. The Contractor will ensure that no pipework
enters electrical rooms or runs above in the vicinity of control panels or electrical panels
The Contractor will lead co-ordination of the building services installation.
The Contractor will include for full production of fully co-ordinated, builders work and
ongoing drawings for all services.
8.16 PROGRAM
The Contractor will submit a detailed time program of works to the Contract Administrator
fourteen calendar days prior to the M&E installation Commencement Date. The
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 105 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
Contractor will also submit a revised Works Program on a weekly basis and/or whenever
the previous Works Program is inconsistent with actual progress or with the Contractor's
obligations.
The Contractor must keep a full set of construction drawings on site at all times. These
drawings must be kept up to date during the course of the installation work with all
alterations, changes and variations, additions and omissions recorded to allow as built
drawings to be prepared.
On final approval by Lidl, the Contractor will prepare and submit to Lidl, a full set of
drawings, for all service systems, showing the final as-installed layouts in AutoCAD disk
format and in hard copy three sets.
On final approval by Lidl, the Contractor will prepare and submit to Lidl, a full Handover
Package, for all electrical and mechanical services in soft copy format and in hard copy
three sets.
8.18 VERIFICATION
The Contractor is to allow for the complete verification of all systems by Lidl. The
Contractor will ensure that Senior Representatives from each of his Sub-Contractors are
available to assist in the verification of the systems. It is anticipated that this work will take
two full working days.
The Contractor will ensure that all systems are fully commissioned and witnessed by the
specialist engineer employed by the MC prior to presentation to Lidl for verification. The
Contractor will make full allowance for the verification of all systems in the development
of their on-site program of works. The building will not be handed over until the verification
is complete to the full satisfaction of Lidl. Verification will include the demonstration of all
air and water flow rates. All control functions and all operation.
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 107 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016
................................................................. .................................................................
Contractor/Lessor/Developer Lidl UK GmbH/Client
Page 108 of 109
LOF Store Specification 2015.1_version 4 JUNE 2016