1
current rating. This is defined as the current which, if applied
Abstract— By its nature, the power generated by offshore wind on a continuous basis, would ensure that the conductor
farms varies substantially with time. Despite this fact, the cable temperature reaches but does not exceed its operational limit.
systems which connect such wind farms back to the onshore grid For the majority of cross-linked polyethylene (XLPE) cables
are typically sized based on a maximum, continuous current in use today, this will equate to 90°C, the maximum
rating. In order to develop techniques by which the sizing of
temperature at which such cables should be operated to give
such cable connections might be optimized, this paper presents a
method for deriving equivalent cyclic load curves from realistic, an acceptably low rate of thermal ageing of the insulation.
time variant generation data. These cyclic load profiles may be If the transient thermal behavior of common export cable
used with the conventional IEC 60853-2 cable rating calculation, systems is considered, the cable thermal response to a step
allowing the cable to be sized for a more realistic duty cycle. The change in load is relatively slow. This is particularly true for
example calculations presented show that this reduction in sections of the route which are the most thermally limiting,
conservatism permits the use of smaller cable sizes, helping to such as deeply buried cable sections at landfalls. The main sea
drive down project costs. The implications of using such methods section of the route is frequently not thermally limiting due to
are discussed, highlighting the tradeoff between cost and lower burial depths and better thermal resistivity compared to
conservatism.
soils at the landfall. In the case studied here, the rating of the
Index Terms-- Power cable insulation, Power transmission, Statistical
cable in the sea bed is 40% higher than at the deeply buried
analysis, Statistical distributions, Underwater cables, Wind energy, landfall section. It will be shown in Section V that achieving
Wind energy integration, Wind farms. the steady state maximum temperature can take 20 years.
Given the inherent intermittency of wind generation, such
I. INTRODUCTION steady state conditions will never in reality be attained. This
leads to the cable being sized for an overly worst case
H IGH voltage AC subsea cables represent a significant
proportion of the capital expenditure associated with
offshore wind farms. As wind farms go further offshore
scenario, which can result in larger conductor sizes than are
truly necessary.
One previous approach to reduce this conservatism is to
and the distance to the landfall of the export cable increases, dynamically predict the transient thermal rating based on the
the proportion of total capital expenditure becomes greater. local weather forecast [4, 5, 6]. This approach has been used
Raising the transmission voltage or moving to HVDC
for overhead lines [7, 8], where such approaches have
transmission both offer the possibility of reducing the number
obtained 120% increase in rating [7]. There is however an
of cables or, at the least, minimising the conductor size of the added complexity of applying these methods to buried cables,
cables needed to carry the rated output of a wind farm. An due to importance of accurately predicting the thermal
alternative approach, and one potentially requiring less of a properties of the burial environment [5]. Whilst these methods
technical advance, is to take advantage of the inherent could be used for wind farm export cables, they do not take
variability of the yield from a wind farm. Numerous published
into account the fluctuating generation of wind farm itself, and
studies have proposed different methods to predict short term
assume a maximum possible circuit load.
and long term wind farm yields from weather forecasts [1, 2,
3]. Whilst these studies have investigated the wind farm yield, B. Overview of Proposed Methodology
they have not considered how the fluctuating yield impacts the This paper begins by defining an example wind farm,
thermal rating of the export circuit. Therefore another followed by a method for the statistical analysis of a wind
approach is to find the appropriate cable size according to the speed time series to obtain an equivalent cyclic load profile for
load that they are likely to experience. use in IEC60853-2 calculations [9]. Although it is a
A. Conventional Cable Sizing Approach generalization to approximate wind farm output by a
cyclically varying load, it is a closer reflection of reality than
The conventional approach to sizing cable systems for assuming a constant output. This equivalent load cycle may
offshore wind farms has been to use a steady state, continuous
then be used to size the export cable, with due consideration
for the thermal behavior of the cable system itself. Such wind
1
R. D. Chippendale, J. A. Pilgrim and P. Cagny are with the Tony Davies speed time series are now commonly used in the evaluation of
High Voltage Laboratory, University of Southampton, SO17 1BJ, UK (e-mail: potential wind farm sites, hence the data is readily available at
jp2@ecs.soton.ac.uk). the design stage of the project. The final part of the paper
S. Catmull and G. Hutton are with RES Offshore, Kings Langley,
Hertfordshire, WD4 8LH, UK (email: simon.catmull@res-offshore.com). compares the predicted cyclic load against traditional ratings,
2
Insulation screen
analyzing the importance of the wind speed assumptions. Insulation Water Tape
Conductor screen Sheath
Conductor Inner Sheath
II. EXAMPLE EXPORT CIRCUIT
The method will be demonstrated by carrying out the initial
sizing of the export system for a hypothetical 300MW
offshore wind farm. Long term historical wind speed data will
be obtained from a meso-scale wind model of the UK and its
surrounding waters [10]. The wind speed data shall be
converted into a time series of wind farm power output using a
generic wind turbine power curve with an appropriate number
of turbines assumed. Account shall be taken of the wake losses
associated with the turbine array, but for the sake of simplicity
it will be assumed that there will be no losses associated with Filler
Armour
the reliability of the turbines or the balance of plant. Serving
A. System Architecture
The transmission architecture will be assumed to be Fig. 2. Simplified cross section of 3 phase export cable
composed of two offshore transformers to step up the array TABLE I
voltage of 33kV to a transmission voltage of 132kV and that Cable dimensions and material properties
an export cable per transformer would be required. The time Volumetric
Thermal
Heat Radius
series of the wind farm power output at 132kV will be Geometry Material Conductivity
Capacity (mm)
converted to a current on the basis that the landfall is the (Wm-1K-1)
(MJm-3K-1)
thermally limiting location and that the reactive power Conductor Copper 320 3.45 20
compensation has been designed so that the power factor at Conductor Semicon
0.5 2.4 21.5
the landfall minimises the power loss. A sketch of the wind Screen XLPE
farm transmission system is shown in Fig. 1. Insulation XLPE 0.286 2.4 38.5
Inulation Semicon
0.5 2.4 40
Screen XLPE
Unknown
Water Tape 0.286 2.4 41.5
Polymer
Sheath Lead 35.3 1.45 43.8
Inner
Semicon PE 0.5 2.4 46
Sheath
Bedding Polypropylene
0.123 1.9 101
and filler yarn
Armour Steel 18 3.8 106.5
Serving PE 0.2 1.7 111
TABLE II
Cable System Properties
Fig. 1. Export system sketch. Parameter Value
Conductor Strand Fill Factor 0.8
B. Cable Systems Conductor Resistivity 1.72 x 10-8 Ωm
Conductor kp 0.8
This study considers a wind farm export system with two Conductor ks 1
export cables which consist of 132kV 3 phase XLPE insulated Conductor Coefficient Of Resistance 3.93 x10-3 K-1
SL-type (each phase in separate lead sheath) cable with Sheath Resistivity 2.14 x 10-7 Ωm
1000mm2 conductors. The three phases are protected and held Sheath Temp Coefficient Of Resistance 4x10-3 K-1
Armour Resistivity 1.38 x 10-7 Ωm
together by layers of PE and steel armour wires. A cross Armour Temp Coeff Of Resistance 4.5 x 10-3 K-1
sectional illustration of the cable layout is presented in Fig. 2. Armour kp 1
The cable dimensions and thermal material properties are Armour ks 1
presented in Table I. The materials properties are considered Relative Permittivity Of Insulation 2.5
as per relevant IEC values, summarized in Table I and II [9]. Insulation Tan Delta 0.001
Voltage of cable 132kV
The filler region is typically comprised of a mixture of plastic Frequency 50Hz
ropes with air voids between the strands. Therefore the
material properties for the filler region are given by a TABLE III
summation of individual material properties weighted by their Seasonal soil and ambient conditions
volume fraction. The burial depth at the landfall is 4m with a Soil
Ambient Air
circuit spacing of 20m. The seasonal soil and ambient Thermal Volumetric
Season Temperature
Conductivity Heat Capacity
conditions are presented in Table III. (Wm-1K-1) (MJm-3K-1)
[ºC]
Summer 0.83 2 15
Winter 0.95 2 10
Dry (above 50ºC) 0.4 1 -
3
lower current level fixed, the high load current (Irate) is then
varied to find the thermal rating of the cable due to the
application of the cyclic load.
Load (A)
Δtrate
Irate
Ilow
Δtlow
Time
Fig. 4. Numerical geometry with boundary conditions Fig. 5. Generic cyclic load profile
assessed via the order of a simple autoregressive time series by considering the probability density function of the wind
model, taking the form speed durations, which is shown in Fig. 10.
𝑣𝑣(𝑡𝑡) = 𝛼𝛼1 𝑣𝑣(𝑡𝑡1 ) + 𝛼𝛼2 𝑣𝑣(𝑡𝑡2 ) + … 𝛼𝛼𝑛𝑛 𝑣𝑣(𝑡𝑡𝑛𝑛 ) + 𝜖𝜖𝑡𝑡 (6)
TABLE V
Fig. 7. Autocorrelation of wind speed data. Distribution of wind speed with different filter lengths
Persistence of periods Persistence of periods
Filter
Length
inside 9-25 m/s range below 9 m/s
(hrs) Mean Max Mean Max
length (hr) length (hr) length (hr) length (hr)
1 13.62 191.00 13.58 293.00
3 21.44 259.00 21.49 387.00
6 28.83 333.00 29.03 448.00
those that caused less. of 6 hrs is presented in Fig.13, which shows that there is a
3. Calculate the rated current (Irate) on the basis of Ilow and continual temperature oscillation due to the cyclic load. The
cycle duration. model is assumed to be in a quasi-steady state when the peak
conductor temperature for each oscillation is approximately
A. Steady State Ratings to IEC60287 constant with neighbouring peaks. The quasi-steady state
The continuous seasonal ratings at the landfall, calculated solution occurs after approximately 15 to 20 years, with the
using IEC 60287, are 604 A in summer and 660 A in winter. oscillation height being approximately 26ºC.
Using (2), it is possible to calculate that the total output load
from the considered wind farm is 1420 A. Assuming this load
is equally divided between the two export cables, each cable
needs to carry 710 A. Based on IEC 60287 continuous ratings
above, it is evident that under this conservative scenario, three
rather than two export cables at 1000mm2 would be required
to avoid exceeding the thermal limit. The incremental cost is
of the order of £1 million per route mile.
Fig. 13. Conductor temperature response due to a cyclic profile with a 6hour
filter length.
basis of the cable temperature is within the reach of present ratings for cables of all voltages, IEC60853-2, 1989
[10] Weather Research and forecasting (WRF): ARW User Guide V3,
technology. It is widely understood within the offshore wind September 2014.
industry that the cost of generation needs to reduce for it to [11] J.F. Ainslie, “Calculating the flowfield in the wake of wind turbines”,
continue to be a viable part of the generation mix. This paper Journal of Wind Engineering and Industrial Aerodynamics, vol 27,
Issues 1–3, pp 213-224 Jan 1988.
has outlined a method by which the cost of a significant
[12] G. Habenicht, “Offshore Wake Modelling” presented at the 10th annual
contributor, the export cables, to the total capital expenditure Renewable UK Offshore Wind conference, Liverpool, England, Jun.
of an offshore wind farm may be reduced. 29-30, 2011.
[13] Electric cables - Calculation of the current rating - Part 1-1: Current
rating equations (100 % load factor) and calculation of losses -
VII. CONCLUSIONS General, IEC60287-1-1, 2006.
A method has been presented for the sizing of a wind farm [14] Current Ratings for Cables, TGN(T)67, 1996.
[15] D. Swaffield, P. L, Lewin, S. Sutton, "Methods for rating directly buried
export cable based on likely generation profiles. This is high voltage cable circuits", IET Generation, Transmission &
achieved through the use of cyclic ratings, where the cyclic Distribution, 2008, page 393-401
load profile is derived through the statistical analysis of long [16] Electric cables - Calculation of the current rating - Part 2: Thermal
resistance, Section 2.1 Calculation of thermal resistance, IEC 60287-2-
term wind time series data. Comparisons between the steady 1, 2006
state and cyclic rating were shown for a thermally challenging [17] E. D. Meyer. (2014, Nov 08). R-Manual. (3.2.0) [Online]. Available:
location section of the subsea cable route for an offshore wind https://stat.ethz.ch/R-manual/R-devel/library/stats/html/decompose.html
farm. The cyclic rating calculated using IEC60853 was shown IX. BIOGRAPHIES
to be in good agreement with results obtained through 2D
FEA. The ampacity increase of 22% as a result of considering Simon Catmull received the Bachelor’s degree in
cyclic ratings over the traditional continuous rating method is Mechatronics from the University of Sussex in 2003 and
then went on to obtain a Master’s degree in Renewable
sufficiently great that the target rating could be met with two Energy Systems and Technologies from Loughborough
export cables of conductor cross-sectional area of 1000mm2. University in 2010. He has been employed by RES
This would remove the need to add an extra cable, or change Offshore since 2010 and currently works as a Project
Engineer supporting the development, construction and
the conductor size for all, or part, of the cable. Although the operation of wind farms on- and offshore.
use of such methods have a clear benefit in terms of reduced
costs, it must be noted that a suitable curtailment strategy must Richard D Chippendale received the Master’s degree in
be in place to mitigate the risk that a period of high power Physics from University of Southampton in 2009. He
generation could be longer than predicted. To fully assess the pursued his doctoral degree at the same university,
investigating the thermal chemical degradation to
cost reduction achieved, it would be necessary to compare the composite materials due to a lightning strike, for which
capital saving with lost production due to output curtailment, he was awarded a PhD in 2013. He is currently employed
for which further development is presently underway. as a Research Fellow, working on a variety of projects
related to high voltage cable systems. He is a member of
IEEE DEIS and an associate member of the IOP.
VIII. REFERENCES
[1] J.W. Taylor, P.E. McSharry, R. Buizza, "Wind Power Density James A. Pilgrim (M’09) received the Bachelor’s degree
Forecasting Using Ensemble Predictions and Time Series Models," in electrical engineering from the University of
Energy Conversion, IEEE Transactions on , vol.24, no.3, pp.775,782, Southampton in 2007, subsequently gaining his PhD in
Sept. 2009 2011 from the same institution. He joined the academic
[2] M.C. Mabel, E. Fernandez, "Estimation of Energy Yield From Wind staff of the University in 2012. His research interests
Farms Using Artificial Neural Networks," Energy Conversion, IEEE include all aspects of high voltage cables and associated
Transactions on , vol.24, no.2, pp.459,464, June 2009 insulation systems. He is actively involved in the
[3] R. Amiri, Wang, Bingsen "A generic framework for wind power development of current rating methodologies, acting as
forecasting", IECON 2011 - 37th Annual Conf on IEEE Industrial the UK member of IEC TC 20 WG19 and Cigre Working
Electronics Society, pg 796 - 801 Group B1.35 “Guide to rating calculations”.
[4] J. Heckenbergerova, J. Hosek, "Dynamic thermal rating of power
transmission lines related to wind energy integration," Environment and Gail Hutton received the Bachelor of Science degree
Electrical Engineering (EEEIC), 2012 11th International Conference from Strathclyde University in 2003, and gained a PhD
on, pp.798,801, May 2012 from the same University in 2008 for research into
[5] R. Olsen, G.J. Anders, J. Holboell, U.S Gudmundsdottir, "Modelling of stochastic models of share prices. She worked for
Dynamic Transmission Cable Temperature Considering Soil-Specific National Air Traffic Services from 2007 to 2010 as a
Heat, Thermal Resistivity, and Precipitation," Power Delivery, IEEE statistician, focusing on the measurement and modelling
Transactions on , vol.28, no.3, pp.1909,1917, July 2013 of aviation risk. She joined RES in 2010, providing
[6] G.J. Anders, A. Napieralski, M. Zubert, M. Orlikowski, "Advanced analysis of technical aspects of wind farm development
modeling techniques for dynamic feeder rating systems," 37th Industry both onshore and offshore and with a particular interest
Applications Conference, vol.2, pp.1012-1019 Oct. 2002 in characterizing uncertainty. She is a member of the Royal Statistical Society
[7] Huu-Minh Nguyen; Lilien, J.-L.; Schell, P., "Dynamic line rating and and has attained both Chartered Statistician and Chartered Scientist status.
ampacity forecasting as the keys to optimise power line assets with the
integration of res. The European project Twenties Demonstration inside Priank Cangy was born in Maputo, Mozambique on
Central Western Europe," Electricity Distribution (CIRED 2013), 22nd the 5th of April, 1993. He is currently studying at the
International Conference and Exhibition on, pp.1- 4, June 213 University of Southampton for an MEng in Electrical
[8] J.K Raniga, R.K. Rayudu, "Dynamic rating of transmission lines-a New Engineering, having recently completed an internship
Zealand experience," Power Engineering Society Winter Meeting, 2000. at the Tony Davies High Voltage Laboratory.
IEEE , vol.4, pp.2403,2409
[9] Calculation of the cyclic and emergency current rating of cables. Part 2:
Cyclic rating of cables greater than 18/30 (36) kV and emergency